Results 1 to 13 of 20
    Dec 2011
    Mid-Atlantic
    Hmm Fuse keeps blowing
    My dad has a heat pump, when the heat is turned on the 3 amp fuse on the 24V red wire off the transformer is blown, a/c is fine. The transformer was replaced, the blower contactor reads 10 ohms across the coil, the backup heat contactor reads 15 ohms. Both work when contactor is pushed in.
    Someone told me that one would check all the low voltage wires to see if they are shorted. Does that mean one would disconnect the wire at both ends (at the thermostat being one end) and then check it to ground, hoping to read OL? Since it's the heat not working, either the white or red wire would be shorted, correct?
    Could it also be a motor problem?
    I'm only a few months deep in this trade and I'm curious.
    it's being caused by a short circuit; now it is in your best interest to ask a co-worker or an instructor to give you guidance on the proper procedure to determine where that short is.
    Quote Originally Posted by dandyme View Post
    good advice!
    do it right the first time!
    New Jersey
    i was taught to remove all control wires, use little popper as a resetable in line fuse
    put amprobe on the 24volt wire at transformer, start attaching one control wire at a time as you energize its appropriate relay you will find the problem soon enough
    “If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton
    I'm learning all the time, the tombstone will be my diploma!!!
    Did you ever stop to think, and forget to start again?
    Dec 2010
    On a Peninsula in NE NC
    I will give this fine piece of advice. Fuses do not go bad.
    You have a direction follow the road stillyout find the trouble
    Nov 2007
    Mississippi
    Is reversing valve energized in heat mode? What brand condenser does your dad have?
    Nov 2011
    You need to determine when the fuse blows: on a call for heat or second stage heat, during defrost, or just when the stat is set to "heat". If it's a Rheem product, could be the reversing valve circuit, since they energize in heat. You appear to have eliminated the aux heat control. Likely not the red wire or the fuse would blow in either mode. Check continuity on the "white" wire to common for low resistance. Based on the info you've provided it's the best bet for now.
    Jun 2012
    nampa idaho
    Might want to check the stat wire for continuity se if there is a short in the stat wire
    Southeastern Pa
    As a new tech, you should apply for pro membership so we can help you in the pro forums. Most technical information is not discussed out here in the open.
    Filing out your profile also helps us know who we are talking to.
    Dec 2011
    Mid-Atlantic
    Update: Someone came to help figure it out and he said it's probably thermostat trouble. We had a new thermostat put in by our local power company for free, which enables them to turn off our power for a short time if needed.
    Do you think it could actually be a faulty thermostat? All the wires seem to be hooked up correctly.
    Also for pro membership I think I need 15 posts correct?
    Oct 2011
    Chicagoland Area
    Screw the blown fuse. THIS
    Quote Originally Posted by JacJak View Post
    would be my concern. I'm curious to the reasoning and if this is something I have to look forward to in Al Gores America.
    Southeastern Pa
    I would say that the recent hookup is more than a coincidence to your problem.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules: