    Quote Originally Posted by dan sw fl View Post
    OR if he doesn't like to be at the mercer of his utility company ...
    Raise it to 78'F / 25.6'C .:. reduce electric cost$ > _ 40%_
    That's true, Dan. But I was attempting to "warm him up" to accepting a higher setpoint at a not so drastic jump.
    • Electricity makes refrigeration happen.
    • Refrigeration makes the HVAC psychrometric process happen.
    • HVAC pyschrometrics is what makes indoor human comfort happen...IF the ducts AND the building envelope cooperate.


    A building is NOT beautiful unless it is also comfortable.

  2. #28
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    6,274
    Quote Originally Posted by Shophound View Post
    That's true, Dan. But I was attempting to "warm him up" to accepting a higher setpoint at a not so drastic jump.
    78'F ought to Feel ABSOLUTELY TERRIFIC when it's 120'F outside. ..!...!!....!!!
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  3. #29
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,221
    Quote Originally Posted by dan sw fl View Post
    1.732 ___ 1.732 .. SQRT 3 for 3-phase power
    12 ___ ___ 12 Amps
    208 ______ 220 V Nice try, did you think I would miss you changing the voltage from 240v down to 220v?
    4323.1 ___ 4572.48 Volt-Amps

    Voltages & Power Factor are not known with certainty.
    There is nothing that even needs to be calculated.
    The Measured power is stated as 4,400 Watts.

    So , if OP wishes one to evaluate the performance as stated in post #1 ( copied below)
    the air flow rate, supply air temperature, model numbers of the condenser and air handlers must also be provided.
    Room temperature and outdoor temperature are provided.
    Relative humidity inside would help, but one can assume it's ~40'F for discussion purposes.


    Unit #1:

    3-Phase, RLA 7.0, Min. Supply Circuit Ampacity 10
    With AC running at 22*C with outdoor temp at 30*C the amp readings were 11-12 amps per phase
    and 12 amps all together including fan

    Wattage measurement with unit set at 20*C with outdoor temp at 30*C (night) = 4400 watts


    Unit #2:

    1-Phase, RLA 13.7, MSCA 19 amps
    With AC running at 22*C with outdoor temp at 30*C the amp reading was
    14 amps and 18 including fan
    Wattage measurement with unit set at 20*C with outdoor temp at 30*C (night) = 3000 watts
    I find it interesting that the power factors are so much different between units. Another oddity is the fact there is 3 phase service to a residential apartment unit, I have never seen 3 phase in house (not including mansions), much less an apartment. I'd be interested to see the watts test/meters/conditions. 3 phase wattmeters aren't exactly common.

    The calculator you linked to is right, and once it proved you are wrong you had to go an fudge the line to neutral voltage from 120v to 110v to try and prove a point. Only after you actually used the calculator and it proved you wrong to you try to discredit the calculator. I even mentioned there are other factors in my previous post BEFORE you posted.

    I wouldn't even care so much if your didn't come with with the flamethrower blazing, laughing at my calculations w/o providing any proof of yours. Highly unprofessional in the AOP forum. At our shop we have a policy never to correct another tech in front of a customer. We talk about it later if there is a disagreement.
    Last edited by 54regcab; 11-02-2012 at 10:18 PM.

  4. #30
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    6,274

    Thumbs up

    Quote Originally Posted by 54regcab View Post
    I find it interesting that the power factors are so much different between units. Another oddity is the fact there is 3 phase service to a residential apartment unit, I have never seen 3 phase in house (not including mansions), much less an apartment. I'd be interested to see the watts test/meters/conditions. 3 phase wattmeters aren't exactly common.

    The calculator you linked to is right, and once it proved you are wrong you had to go an fudge the line to neutral voltage from 120v to 110v to try and prove a point. Only after you actually used the calculator and it proved you wrong to you try to discredit the calculator. I even mentioned there are other factors in my previous post BEFORE you posted.

    I wouldn't even care so much if your didn't come with with the flamethrower blazing, laughing at my calculations w/o providing any proof of yours. Highly unprofessional in the AOP forum. At our shop we have a policy never to correct another tech in front of a customer. We talk about it later if there is a disagreement.
    It's been an interesting thread observing this discussion that you are having with yourself on the methods and necessity of a calculation.

    The real point is that the OP has not provided nearly enough information on the electric usage, building envelope, maximum environmental condition and unit model numbers to make an independent determination and overall validation of what one might expect in operating cost$.

    More than 7,000 total watts for 1,200 square foot residence is not what one would normally ( or ever?) see in the U.S.
    The OP wishing for 68'F in the desert can not be achieved in an economical manner based on normal U.S. electric rates..
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event