oil primary control
ok i know you all are gonna say have a real tech go out and check but i am a real tech just real inexpirenced at oil. i just started messing with oil furnaces and doing maintenances and some repairs.
but my neighbor came over saying their heater isnt working. i walked over and checked it out, they turned it on from the t-stat and the blower came on which was normal. but then that was it and my first question is how the hell do you reset the new primary controller? it doesnt have a reset button all it has is an up and down arrows and an "i" button. i figured id ask here first and im gonna talk it over with my field sup tomorrow. i didnt bring my tool bag over or anything so i know many things could be the problem and im gonna dive into it tomorrow after work im just wondering about this new primary control ive never seen
thanks in advanced
(just tryin to learn and help a neighbor out)
-
10-31-2012, 10:42 PM #2
If you are talking about the Honwywell R7284 series-
• Soft Lockout: Caused by a temporary internal error
such as low voltage. The control recovers
automatically after the error is no longer detected.
• Hard Lockout: Caused by a failure internal to the
control or by a system fault such as flame out of
sequence. A Hard Lockout will result in a no heat
condition. To reset from Hard Lockout press and hold
the “i” button for 2 seconds.
• Restricted Lockout: Caused by a number of
consecutive hard lockouts on the same heat cycle. To
reset from a Restricted Lockout press and hold the “i”
button for ten seconds.
Here is a link to the Installation Manual -
http://s3.pexsupply.com/manuals/1281..._PROD_FILE.pdf
"I don't know why it be like it is, but it do"
-
11-01-2012, 06:10 AM #3
Professional Member
- Join Date
- Jun 2012
- Location
- rising sun, md
- Posts
- 70
-
11-03-2012, 12:52 PM #4
Professional Member*
- Join Date
- Jul 2000
- Location
- Northern Wisconsin
- Posts
- 1,566
First most important thing to learn about oil furnaces. If you have to reset the primary control DO NOT place yourself in front of the furnace when it tries to fire.
Second most important rule is to never tell or show the customer how to reset the primary control because they will most always lie to you about how many times they pushed it (and the burner didn't light) before they called you. If you suspect this is the case....... read the first most important thing to know about oil furnaces.
Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.
-
11-03-2012, 07:20 PM #5
Professional Member
- Join Date
- Jul 2012
- Location
- CT
- Posts
- 141
-
11-03-2012, 07:41 PM #6
Professional Member
- Join Date
- May 2002
- Location
- evansville indiana
- Posts
- 892
I no longer service oil ...
Back in the day when the HO said they didn't reset it I would automatically look for excessive oil if possible . Then reset it and stay the hell out of the way . I Remember having to shut them off and let them burn out ,with the inddor blower running of course .
I don't miss oil a bitmikeacman
-
11-04-2012, 08:23 AM #7
Professional Member
- Join Date
- Sep 2012
- Location
- Ottawa, Canada
- Posts
- 28
I would read the link rchristie420 sent. I always read the manual before I work on new systems and it saves a lot of headaches. My parents have oil and I tell them to call me before they touch anything.
-
11-04-2012, 09:10 AM #8
Before you do anything, change the nozzle and fuel filter. This usually solves the problem and is needed every year.
UA LU189
10mm, because it's better than .45acp
-
11-06-2012, 12:56 PM #9
Regular Guest
- Join Date
- Jul 2012
- Location
- west-central pa
- Posts
- 9
You gotta watch out for the barometric damper. Had them blow across the basement when the HO only pressed the reset once and called for service.
-
11-06-2012, 01:15 PM #10
#1 always check for unburnt oil. If there is try and burn it off with a lit piece of paper or something.
-
11-06-2012, 09:00 PM #11
Professional Member
- Join Date
- Jun 2012
- Location
- rising sun, md
- Posts
- 70
yeah when i go on a service call for oil(which has only been about three timeso far)i light a piece of paper towel and throw it into the heat exchanger to burn off any oil in there slowly instead of having the big bang and the HO thinking you blowing their house up lol
-