    Hey guys I was just installing this trans in a split unit system and when you cycle the a/c to on the fan is spinning slower than it should as soon as the cool shuts off then the speed of the fan kicks up again. while i was installing it I accidently wired it for 240 and the trans hummed really loud so i shut it off and wired it for 120 now it seems as if I have degraded the life of the trans when it hummed so loud. So Im thinking that the trans can do the fan fine but, when i switch the unit to on and the trans has to provide for the thermostat and the contactor and the fan it just cant do it all now. what do you guys think?

    shaun a\c man

  2. #2
    That 24VAC secondary, guessing here, became a 48 VAC secondary for the duration of the mis-wire. Hard to tell what got damaged or degraded.

  3. #3
    Join Date
    Feb 2005
    Posts
    344

    acman0001

    It sounds like you are energizing more than one blower speed at the same time. Better check the wiring and/or board.

    The tranformer does not supply power for the blower. The over voltage probably damaged the control board if there is one.

    Pull the lead for the heat speed and see if the blower runs normally in cooling.

    Good luck...

  4. #4
    Join Date
    Oct 2004
    Posts
    3,400
    If he had 120v power supply, and hooked up a 240v tap from the transformer, wouldn't he have had only 12 volts?



  5. #5
    Join Date
    Feb 2005
    Posts
    344

    wildleg

    Sounds good to me. In any case check for two speeds trying to run at the same time,

  6. #6
    Maybe I'm missing something.....but why didn't you run 240? By split do you mean you were wiring the A/H up? If so...then I assume most are wired 240. You need to add that other leg for it to work. Are you wiring the high voltage into the heat strips or into the trans?

  7. #7
    Join Date
    Oct 2004
    Posts
    3,400
    From his original post, I assumed his indoor section was a gas furnace, supplied with 120v. He had installed a one-size-fits-all multitap transformer, and inadvertedly chosen the wrong tap.

    If it is an electric furnace, then he needs the 240 volt tap, as he is now furnishing 48 volts.

    He's still got problems, but I don't think they are from a bad transformer. (I guess it could be, if the transformer is not developing 24 volts.)

    I have to ask, what killed the first transformer?

  8. #8
    Join Date
    Jun 2003
    Location
    Florida
    Posts
    9,548
    Originally posted by acman0001
    Hey guys I was just installing this trans in a split unit system and when you cycle the a/c to on the fan is spinning slower than it should as soon as the cool shuts off then the speed of the fan kicks up again. while i was installing it I accidently wired it for 240 and the trans hummed really loud so i shut it off and wired it for 120 now it seems as if I have degraded the life of the trans when it hummed so loud. So Im thinking that the trans can do the fan fine but, when i switch the unit to on and the trans has to provide for the thermostat and the contactor and the fan it just cant do it all now. what do you guys think?

    shaun a\c man

    After reading this post all I can say is WTF??? A/C shuts off, blower speeds up. Transformer has nothing to do with blower speed. You need to call a pro before you fry something.
    If everything was always done "by the book"....the book would never change.

  9. #9
    Join Date
    Jan 2001
    Posts
    8,225
    People should really be clearer in their posts... split system sounds like a heat pump but could very well be a furnace and blower..

    There should be a top posted and sticky post at the top of each section that tells the people contemplating posting a question that they need to be as detailed and specific as possible so that folks on here who are willing to help can give the best possible answer or solution.

  10. #10
    Wild leg:

    Transformer lesson using easy numbers.

    V1/V2 = N1/N2 where N1/N2 is the turns ratio.

    Say we have a transformer 125V:25V or a ratio of 5:1, so it steps down by a ratio of 1/5.

    So if we apply 250 V and we step down by a factor of 5, the secondary would be 250/5 or 50 volts.

    Transformers are perfectly happy working the other way to0. The same transformer can step up 25 volts to 125 volts if you reverse the primary and secondary. You can wire the secondaries in series and parallel. In parallel the secondaies must be the same voltage and the available current will be the sum of both. In series, the voltages can add or subtract depending on phase.

  11. #11
    Join Date
    May 2006
    Location
    Philadelphia, PA
    Posts
    1,398
    I think an experienced technician is needed here to see what's going on.
    Climate Control Solutions for your Home or Office

    Serving Northeast Philadelphia and Surrounding Areas

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event