    We are installing a 10ton Carrier heat pump split unit system.(R410A) The compressor located on the 8th floor and the fan coil located on the ground floor. Is this require to have liquid solenoid valve?

    Also, for the above system the liquid line 1/2 suction line 1 1/8. The install guy use 5/8 for the liquid line and 1 3/8 for the suction. What kind of problem we will face with the over size piping and how can we correct the problem if we can't replace the piping?

    Thanks.

  2. #2
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,635
    1-what does install manual indicate pertaining to LLS?

    2-got a model #
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  3. #3
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    1,439
    The piping is likely not oversized for the application you have likely over a 100 ft lineset.

    With the compressor on the roof, the biggest issue will be oil return. Is this r22 or 410a. If 410a, the oil return will be less troublesome due to POE oils ability to mix with vapor refrigerant. If R22, then you will need a suction line trap at the base of the riser, and every 20 ft of vertical rise, and an inverted trap at the very top of the riser. The LL solenoid is a good idea to aid in the prevention of refrigerant migration.

    But, check with the OEM, and request a long lineset application supplement.

  4. #4
    Join Date
    Oct 2005
    Location
    Phoenix, Arizona
    Posts
    353
    Your best bet would be to contact Carrier tech support or read the installation manual. Like heatingman said a LL valve would be a good idea
    RTFM!!!

  5. #5
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,727
    The liquid line will hold 4 plus extra pounds of charge. The vapor line will hold almost an extra pound of charge. Suction velocity will be border line at only 1344FPM, which is ok. A solenoid to help prevent migration would be a good accessory.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event