    Remote operation of york chiller

    I am trying to start and stop a york max-e centrifugal chiller remotely via a BMS. Wiring diagram shows terminals 1, 7 and 8 on the I/O board. The control source on the optiview display is currently showing local. All I am doing with the terminals on the I/O board is closing a set of contacts on my BMS and sening the signal back. This seams to be digital to me. My York tech is telling me Analog. The wiring diagram says the chiller must be in remote mode, but remote is not a choice. The choices are local, digital, analog, and YSN. I think it should be digital. What do you guys think? I would like to trust my service guy but his explaination just seems wrong.

  2. #2
    Join Date
    Jun 2011
    Location
    Detroit, MI
    Posts
    67
    Hi there...If I am not mistaken, you need to set the control source to digital, then close 1 and 7 (with 1 and 8 open) to start and clost 1 and 8 (with 1 and 7 open) to stop- a set of spdt contacts work great. In local mode, these contacts don't do anything- the chiller controls its self from internal schedule, or if that's not set, the black rocker switch. Which, by the way, the rocker has to be in the run position to use the digital mode. Basicly, it's "remote digital" and "remote analog." If it has an ISN setting for the control source, that was for some propietary stuff York had...not usre it's still around or not.

  3. #3
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,618
    Quote Originally Posted by Cadrion View Post
    Hi there...If I am not mistaken, you need to set the control source to digital, then close 1 and 7 (with 1 and 8 open) to start and clost 1 and 8 (with 1 and 7 open) to stop- a set of spdt contacts work great. In local mode, these contacts don't do anything- the chiller controls its self from internal schedule, or if that's not set, the black rocker switch. Which, by the way, the rocker has to be in the run position to use the digital mode. Basicly, it's "remote digital" and "remote analog." If it has an ISN setting for the control source, that was for some propietary stuff York had...not usre it's still around or not.
    Sounds like we have a winner. I concur
    Arguing with your Boss is like wrestling with a pig in
    mud.
    After a while you realize that while you are getting
    dirty, the pig is actually enjoying it.

    It is not exactly cheating, I prefer to consider it
    creative problem solving.

    25 years ago we had Bob Hope , Steve Jobs , and Johnny Cash today we have no Hope no Jobs and no Cash !
    I can fix broke but i can't fix stupid !

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event