    correct value Starting capacitor should i use

    i have 280uf Starting capacitor that i was thinking to replace the blown capacitor. the blown capacitor value is 125uf.
    is it ok to use this one


    125uf http://www.frigorie-climatisation.co...oss/nl10mf.pdf
    280uf http://www.ra.danfoss.com/TechnicalI...3_Cd43d522.pdf

  2. #2
    Join Date
    Nov 2007
    Location
    Tucson, AZ
    Posts
    126
    I would use what it came with are you changing the potential relay too? I would never replace just a start capacitor alone.. get the kit..
    What took the capacitor out.. did it stay in the system, do you know how to check it and see when it drops out? the root problem is not the capacitor that is the symptom..
    Bruce

  3. #3
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,540
    No, its not ok. You posted the spces on 2 different voltage compressors. can't compare them.