Results 1 to 10 of 10
  1. #1
    Join Date
    Jul 2006
    Posts
    614
    Post Likes

    HP AUX HEAT does not shut off until Tstat set point

    I just finished a complete geothermal install. This issue is kicking my butt. This system has a single stage compressor with 15 K of thermal B/U heat.

    The Tstat is a WF model TP32U03 3 stage heat 2 stage cool.

    My question is: The aux heat turns on at 3 degrees above room temp. The aux heat will not turn off until the tstat room temp setpoint is satisfied and the heat pump shuts off. Is this aux heat "turn off" a function of the tstat or the WSHP mother board? I tried programming the tstat, I can get the aux heat "turn on" temp to be delayed until 7 degrees above room temp vice 3 degrees, but the aux heat still stays turned ON until the tstat\room temperature is satisfied. Shouldnt the aux heat turn off within 2 degrees above the tstat (room) temp? Is this normal operation for some tstats?

    On another note, on this single stage compressor system, Y2 heating just bumps up the speed of the X13 ECM motor a little bit. What is the purpose\gain of that? I mean, if I'm losing heat in the structure calling Y1, why would I want to add AHU cfm without additional heat?

    Thanks

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    38,872
    Post Likes
    If the geo is single stage, Y2 shouldn't be hooked up. I suppose it is possible that the geo uses the same board for both single stage and 2 stage where high needs a tad more airflow.

    I have heard of stats that can be set to leave backup on until both stages are satisfied. Rare. But only thing I can think of besides a defective stat. Look through your advanced setup options.

  3. #3
    Join Date
    Dec 2007
    Posts
    7,152
    Post Likes
    Not sure if this applies, but;

    some stats have a feature that will allow it to "... finish on high fire/stage". I take this to mean that it will ramp down instead of continuing on max. This is a stat setting.

    as for the fan, on product we install(our installers and many techs don't get this) if you have a single stage unit on a two stage board and Y1/Y2 are connected(by jumper or internal) then it runs Y2 blower speed. you MAY, like on our product, be able to separate Y1 & Y2 and connect to Y1 only and get its speed. This is on the unit board for us.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  4. #4
    Join Date
    Jul 2007
    Location
    New Jersey
    Posts
    3,035
    Post Likes
    the possiblity that a little tweekage in the tstats installer set-up mode may help
    “If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton


    I'm learning all the time, the tombstone will be my diploma!!!


    Did you ever stop to think, and forget to start again?

  5. #5
    Join Date
    May 2009
    Location
    Cumming, GA
    Posts
    1,900
    Post Likes
    Check the link below. Page 5 under "smart heating". If "on", It states once the aux heat is energized, the aux heat will stay energized until thermostat is satisfied regardless of demand/differential.

    http://www.waterfurnace.com/thermostats/TP32U03-5.pdf

  6. #6
    Join Date
    Jul 2006
    Posts
    614
    Post Likes
    Thread Starter
    Quote Originally Posted by Brent Ridley View Post
    Check the link below. Page 5 under "smart heating". If "on", It states once the aux heat is energized, the aux heat will stay energized until thermostat is satisfied regardless of demand/differential.

    http://www.waterfurnace.com/thermostats/TP32U03-5.pdf
    Thank you all for the responces. Yes, this is set to "off". I called WF, they said this is the normal function of this Tstat, keep aux heat on until set temp is satisfied.

  7. #7
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    38,872
    Post Likes
    I sure wouldn't want that. Can you turn it so backup only runs when needed? Will save you juice!

  8. #8
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Quote Originally Posted by BaldLoonie View Post
    I sure wouldn't want that. Can you turn it so backup only runs when needed? Will save you juice!
    +1 !!!

  9. #9
    Join Date
    Jul 2007
    Location
    New Jersey
    Posts
    3,035
    Post Likes
    Quote Originally Posted by riderman View Post
    Thank you all for the responces. Yes, this is set to "off". I called WF, they said this is the normal function of this Tstat, keep aux heat on until set temp is satisfied.
    hmmm, sounds a little sketchy
    “If I have seen further than others, it is by standing upon the shoulders of giants.” ~ Sir Isaac Newton


    I'm learning all the time, the tombstone will be my diploma!!!


    Did you ever stop to think, and forget to start again?

  10. #10
    Join Date
    Sep 2012
    Location
    Ottawa, Canada
    Posts
    28
    Post Likes
    Its your energy to waste, if wf says its normal I would go with the company. We use to have things called anticipators when i was a kid, wait I still am:]

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums