    I've seen one before, just didn't remember it.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  2. #42
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    Thread Starter
    Here is the one that York is supplying here. Name:  ImageUploadedByTapatalk1351883091.890684.jpg
Views: 629
Size:  47.6 KBName:  ImageUploadedByTapatalk1351883105.527156.jpg
Views: 599
Size:  38.9 KB


    Sent from my iPhone 4s
    using Tapatalk
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  3. #43
    Join Date
    Mar 2011
    Location
    Long Beach, CA
    Posts
    492
    Post Likes
    So whats it not doing now.

  4. #44
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    Thread Starter
    Quote Originally Posted by alcomech View Post
    So whats it not doing now.
    I have not heard from him so it must be working ok.


    Sent from my iPad using Tapatalk HD
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  5. #45
    Join Date
    Jun 2011
    Location
    Detroit vicinity, Michigan
    Posts
    79
    Post Likes
    Replace the roll-out switch. This is a common problem with these units. You will read continuity, and 24V through the switch to the R.O. terminal, but it will not pass the proper current to operate the board.

    I was that kid once. Now I replace it with every failed module.

  6. #46
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by Workin4TheMan View Post
    Replace the roll-out switch. This is a common problem with these units. You will read continuity, and 24V through the switch to the R.O. terminal, but it will not pass the proper current to operate the board.

    I was that kid once. Now I replace it with every failed module.
    When the switch has limited current capability, you can read a voltage drop across the rollout switch when the circuit is energized.

    Replacement of the rollout with the module IS a good idea.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  7. #47
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    I've always used the Honeywell with the continuous retry to prevent nuisance lockouts. Just needs a little rewiring.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  8. #48
    Join Date
    Sep 2012
    Location
    Ottawa, Canada
    Posts
    28
    Post Likes
    I had a similar call with no ignition, and was told it was running motor due to venting failure. I am still waiting for final answer from my boss this week as they replaced venting on friday.

+ Reply to Thread
Page 3 of 3 FirstFirst 123

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •