Results 27 to 39 of 48
  1. #27
    Salt Lake City/Tooele
    When the RTU has horizontal duct you have to remove the top panel and inner HX panel to get to the primary and secondary switches. Real PIA.
  2. #28
    Ask him if he found that sequencer inside the side discharge panel(back panel). If so he reset teh high limit, which will trip if you shut the disconnect off during a heat call with teh burner running.
  3. #29
    Oct 2011
    Chicagoland Area
    You talking about the 3 wire limit correct?
  4. #30
    Dec 2008
    Buffalo NY
    This was in the control panel with the contactors and relays. I know about the limit by the heat exchanger. That was the first thing I had suggested.
    Join http://scopeny.org/ Shooter’s Committee on Political Education
    The world is full of sheep,try not to join the flock.
    Support the Skilled Trades, Don't DIY
  5. #31
    yep.
  6. #32
    Dec 2008
    Buffalo NY
    After looking at the wiring diagram I think he was talking about the ETD. Electronic Time Delay.
  7. #33
    Oct 2011
    Chicagoland Area
    I reread the post. Sounds like the initial problem is/was the crossover tube and/or clogged pilot orifice and/or spiders nest. This is why he had to light with a torch. Does this unit have the blue Johnson Controls ignition modules? Those are designed to have multiple voltage inputs for them to fire. Even though you have 24v at TH, if any limits are open the inducer will run but you will not get spark.
  8. #34
    Dec 2008
    Buffalo NY
    He said they were grey boxes which means they were replaced. I think those are UEI boxes?
  9. #35
    Oct 2011
    Chicagoland Area
    Not familiar with UEI the Honeywell universal is grey, and I thought JC did make grey boxes at some point in time but I could be wrong.
  10. #36
    Dec 2008
    Buffalo NY
    I have one in my truck. I will check tomorrow and let you know the make. I know it's the JCI replacement.
    Sent from my iPhone 4s
    using Tapatalk
  11. #37
    up in the hizzy
    Call P&J !! we fix it the first time!!
  12. #38
    Southeastern Pa
    The JCI replacement is the black UEI box.
    2 Tim 3:16-17
    AOP Forum Rules:
  13. #39
    Dec 2008
    Buffalo NY
    Quote Originally Posted by valdelocc View Post
    That's funny this guy is from P&J and said he learned everything he knows from you. All kidding aside, I just wanted to get the kid some other thoughts on the issue since I knew I would probably not have time to go down and check out his issue. But he figured it out and learned a little from it.