Results 1 to 13 of 16
    Oct 2012
    Poor Heating and Cooling Question
    I have 4" duct running 15 feet off main trunk to a 12x12 bedroom with no return line. Would increasing it to 6" make a huge difference? It would require opening up a drywalled cealing and lots of labor repairing plaster. The other option would be a plug in heater but would not solve my a/c problems during the summer. Temp differences from the living room to bedroom are 70 degrees vs 60 degrees. Half my basement is unfinished and I ran 6" to other rooms with dramatic improvement but those rooms have a return.
    SW FL
    ____ _ 6" needed + Add returns!
    80 CFM in 6" duct =~ 400 FPM which yields a Good Design..
    Designer Dan
    Cincinnati, Oh
    Quote Originally Posted by powertower View Post
    Have someone come out and take a look for ya.
    "Just get it done son."
    Dad adjusted
    Oct 2010
    Might be easier to abandon the 4" duct and seal it off then run a new 6 so you don't have to pull down Sheetrock
    SW FL
    4" might provide 30 cfm. 6" diameter flexible duct x 15 foot straight would likely be capable of ~80 CFM with a return.
    Designer Dan
    Saint Joseph, MI
    The only time a small 4" duct is appropriate is in small spaces like walk-in closets and small bathrooms. With ductwork, bigger is usually better as long as you select the proper register size for adequate throw (mixing of air). You can always use dampers on a branch to reduce air flow if you have too much.
    Aug 2009
    Beatrice, NE
    What is the rest of your system? I have run into houses where every run was 4". They were called "Blendaire" systems if I remember correctly. They worked great with the origional equipment that had a high static blower. Once that equipment was replaced they didn't always work so well.
    Having said that if the whole house is done in 4" then the entire duct system needs to be replace to get it to work with the present equipment, that would include boots and registers.
    SW Wisconsin
    I have 4" duct running 15 feet off main trunk to a 12x12 [144-sf] bedroom with no return line. Would increasing it to 6" make a huge difference? It would require opening up a drywalled ceiling and lots of labor repairing plaster.
    The amount of CFM airflow required to a room depends on the required heating & A/C Btuh requirements of each individual room.
    Depending on the actual Heating & Cooling Design Btuh load of the room for your individual situation; that could easily range from less than .50% of the sf to slightly 'over' one to one CFM per sf of the room.
    Therefore, you need the room by room Btuh requirements for both heat & A/C. For A/C, you can divide the Btuh requirement by 30 (12,000-Btuh / 400-CFM is 30 for cooling).
    (Example: Room design is 2500-Btuh / 30 = 83-CFM - a 6" metal RD duct; then select a diffuser providing the needed velocity throw & pattern spread)
    Example: you size the duct run to the highest CFM requirement, "with dampers installed at the take-offs."
    Okay; let's say the 144-sf room requires 85% of that sf to cool the room or, 122-CFM. If 60% of the footage, it's 86-CFM; you need to know the Btuh calc required for that individual room.
    A heating & cooling load calc is a requirement for accurate duct sizing & total airflow engineering design work.
    Returns need to equal supplies...
    Udarrell always offers very good info and explains it well.
    May 2008
    Central Fla.
    Just ran some quick/rough calcs. they come out to 7-7.5" duct needed to supply the right amount of air if your ceilings are 8'.
    SW FL
    Quote Originally Posted by TwincamDave View Post
    OK, I'll take the 7.5" duct.
    Designer Dan
    Jul 2012
    Western KY
    Hold on every one. If you just go in and start changing, adding, taking away supply runs you are changing the entire system. You'll have your airflow all out of whack. End up chasing hot and cold spots all over the house. A duct system should be designed based on load and equipment. If its not you can't get there from here. I recommend an evaluation of the system to determine what you need and where you need it prior to making any further changes. Fix it once and be done. Otherwise you will end up fixing on it forever. IMO.
    SW Wisconsin
    If you're using air changes per hour (ACH) criteria, then I'd use 6-ACH to that room which yields 115.2-CFM using a 7" rd metal duct yields around 432-fpm velocity, using a proper diffuser should be enabled to get proper throw & spread.
    Using a 6" RD metal duct the velocity would be 587-fpm; still under 600-fpm.
    When sizing duct I normally use 460-CFM per ton of cooling or, a factor of 26 with which to divide the cooling Btuh; some in hot dry climates use as high as 500-CFM per ton which is a factor of 24.