Did you check that the gas meter was maybe locked off ?
Use your manometer on the outlet (manifold) side of the gasvalve, you should have approx 3.5 in wc and between 3.2 to 3.8 in wc per the manufactors label.
If you have gas pressure thats good, but indicates an issue with ignition = ie: bad burners, crossovers, bug in orifice, air flow past ignitior gasket, and ect.
luck dan
ps - stay around, maybe we can learn you a little bit.
-
10-30-2012, 08:53 PM #17
-
10-30-2012, 08:55 PM #18
-
10-30-2012, 09:08 PM #19
I like this guy!
most natural gas manifold pressures will be 3-3.5" wc
"wc is defined as the pressure exerted by a column of water of 1 inch in height
one pound pressure per square inch will lift a column of water 2.31 ft or 27.7"
inversley .433 psi will lift a column of water one foot. we usually round it off to 1/2.
most residential gas valves and regulators are rated at 1/2 lb pressure inlet max.
that would be about 14" wc
In North America, air and other industrial gasses are often measured in inches of water when at low pressure. This is in contrast to inches of mercury or psi for larger pressures. It is also used in natural gas distribution for measuring utilization pressure (U.P., i.e. the residential point of use) which is typically between 6 and 7 inches WC (6~7" WC) or about 0.25 psi.
.36 psi, or 27.7 in≈ 1 psi.
in my area most residential areas are around 7"wc. entering
hopefully you have a 1/4" plug entering the gas valve?
some gas valves have an 1/8" or 1/4" plug
I am old and always use an actual manometer.
I also use a digital testo to verify.
jp is right
you gotta start somewhere!
good luck!
Frank
I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!
-
10-30-2012, 09:08 PM #20it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair
-
10-30-2012, 09:20 PM #21
-
10-30-2012, 09:25 PM #22
-
10-30-2012, 09:28 PM #23
-
10-30-2012, 09:29 PM #24
i still use mercury!!!!!!!!!!!!
i collect old stats so i can refill all my manometers!I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!
-
10-30-2012, 09:31 PM #25
-
10-30-2012, 09:32 PM #26



Reply With Quote