    Hi guys, i have very well insulated residential building where district cooling system and fan coil units are used for air conditioning. Due to high performance of the heat insulation used, the cooling load calculated were very low. when i came to selecting the fan coil unit in each room, i had to choose ones of capacities that are higher than the cooling load of the room by around 50%. The heat exchangers and water pumps are sized based on the calculated cooling load. Now, the problem is that the chilled water flow of the system is 50% less than the chilled water flow required by sum of all fan coil units. i know fan coil units wouldn't work all together but I'm still concerned about some issues that may arise due to this big difference between calculated loads and selected fan coil unit capacities. Please note that I'm using variable speed pump with two way valve for each fan coil.
    is there any problem with such system, your advise is highly appreciated
    Thanks,

  2. #2
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    8,142
    Post Likes
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  3. #3
    Join Date
    Apr 2010
    Posts
    7
    Post Likes
    Thread Starter
    Quote Originally Posted by dan sw fl View Post
    Thanks dan for your reply, i did detailed calculation and the envelope is defined, i had to go for a fan coil unit which is double the cooling load of the room because it was the smallest one available and i don't want two rooms to share same fan coil unit. the building is huge one of 30 stories and i have hundreds of fan coil units. i have also another concern about the fresh air handling unit, since the system chilled water flow is less than whats required by total fan coil units, this may create a shortage in water flow required by fresh air handling unit which would affect the ability of the coil to remove moisture.

  4. #4
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    8,142
    Post Likes
    Quote Originally Posted by rami_9630 View Post
    Thanks dan for your reply, i did detailed calculation and the envelope is defined, i had to go for a fan coil unit which is double the cooling load of the room because it was the smallest one available and i don't want two rooms to share same fan coil unit. the building is huge one of 30 stories and i have hundreds of fan coil units.
    So you are an Expert on Chilled Water System Design and there won't be an issue since the design will have MULTIPLE reviews and challenges by other experienced professional engineers and inspectors prior to sizing the chiller, pumps, piping, controls, set-up and commissioning. Sounds like VRV systems would be appropriate.

    I cannot even imagine how small the rooms are going to be, must be < ~200 square feet.
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  5. #5
    Join Date
    Jan 2009
    Location
    Saint Joseph, MI
    Posts
    5,564
    Post Likes
    I'm agreeing. Rather than a fan coil, it seems like VRV unit utilizing 1 air handler for each space with hot water reheat might be appropriate maybe using hot water reheat at each VRV.

  6. #6
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    8,288
    Post Likes
    Quote Originally Posted by rami_9630 View Post
    Thanks dan for your reply, i did detailed calculation and the envelope is defined, i had to go for a fan coil unit which is double the cooling load of the room because it was the smallest one available and i don't want two rooms to share same fan coil unit. the building is huge one of 30 stories and i have hundreds of fan coil units. i have also another concern about the fresh air handling unit, since the system chilled water flow is less than whats required by total fan coil units, this may create a shortage in water flow required by fresh air handling unit which would affect the ability of the coil to remove moisture.
    Currently involved in a retirement center with a similar problem. They are supplementing their make-up air system with several large dehumidifiers. Their chilled water in not cold enough and the cooling load not high enough to get down to <50%RH. They had +65%RH commonly in the isolated rooms when the outdoor dew points were +55^F. The removal of moisture is dependent on the chilled water temp leaving the cooling coil and the length of the coiling cycle.
    The fix is to thoroughly dry the incomming fresh air (<45^F dew point) and provide extra dehumidification to all the open parts of the space. Reheat without a very cold chill water will provide <50%RH. Reheating only make the chilled water system warmer which removes less moisture. This is critical in green grass climates.
    Regards TB
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  7. #7
    Join Date
    Apr 2010
    Posts
    7
    Post Likes
    Thread Starter
    the room not very small but the load is, the building can fit for leed rating due to superior characteristics of the envelope, the glass u-value is 1.8 w/m2k, SC=25 and wall u-value is 0.3 w/m2k, so you can imagine how small loads can be.

  8. #8
    Join Date
    Apr 2010
    Posts
    7
    Post Likes
    Thread Starter
    thank you all for replying, im thinking of adding secondary pumps of flow capacities higher than the primary pumps to deal with flow demands of fan coil units. i am not sure if secondary pumps flow can be greater than primary flow, any ideas?

  9. #9
    Join Date
    Jan 2009
    Location
    Saint Joseph, MI
    Posts
    5,564
    Post Likes
    Is there a storage tank seperating the primary and secondary? If so, I dont see a problem. In com/ind with multiple chillers you size primary pumps for each chiller then secondary pumps for the cw loop. But you normally have a storavge tank to provide some resonance to reduce short cycling. At
    Least thats how I understand it.

    It could be 2 or 3x the flow for whst it matters. Buy the delta of course would be smaller since capacity is seyt by the chiller.