Size matters not sure there is enough room to stick 2 compressors in there for the foot print of the unit I agree with #2 sometimes chillers are oversized. Since most copeland tandems come as a complete unit cost cancels out. Dealing with smaller chillers like that most of the jobs are not professionally engineered it more of a rough guestimate.
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
10-31-2012, 11:42 PM #28
-
10-31-2012, 11:53 PM #29
Professional Member
- Join Date
- Jan 2005
- Posts
- 587
-
10-31-2012, 11:58 PM #30
-
11-01-2012, 12:16 AM #31
Professional Member
- Join Date
- Jan 2005
- Posts
- 587
-
11-01-2012, 01:51 AM #32
-
11-01-2012, 05:53 PM #33
Professional Member
- Join Date
- Jan 2005
- Posts
- 587
-
11-01-2012, 05:57 PM #34
Professional Member*
- Join Date
- Aug 2002
- Location
- Greenville SC
- Posts
- 398
With the Micro coils the head will spike at startup then come back down to normal operating conditions. On a hot day it should not spike much over five hundred psig. If you must weigh in the charge subtact about five percent of what it says on the tag. If you overcharge just a little, it will trip. There should be a charging procedure in the OM book, that is the best way to charge it up. Again, if you have any restriction in the drier you will have problems.
-
11-01-2012, 06:06 PM #35
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,514
-
11-01-2012, 06:06 PM #36
-
11-01-2012, 06:13 PM #37
-
11-01-2012, 06:22 PM #38
-
11-01-2012, 08:28 PM #39
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,514




Reply With Quote