Page 2 of 6 FirstFirst 123456 LastLast
Results 14 to 26 of 72
  1. #14
    Join Date
    Mar 2007
    Posts
    3,646
    Post Likes
    Thread Starter
    Quote Originally Posted by Nuclrchiller View Post
    I've never seen that bearing bracket removed while the motor is still mounted to the discharge volute. Do you plan to replace the motor-to-volute o-ring? How about the discharge volute-to-condensor o-ring? Appreciate the pics. Very nice equipment room... once you get past the chilled water lines above the starter.
    It is a lot easier to do that front bearing bracket with the thrust bearings removed, or at the very least, with the thrust bearing support removed. It is even easier still to do it all with the motor sitting on a cart on the ground.

    It is a nice, well lit mechanical room with a lot of clearance and room to work without interference. The guys and gals at this site work very hard to keep everything in good order.
    The key to happiness is lower expectations.

    Don't pick the fly crap out of the pepper.

  2. #15
    Join Date
    Jun 2012
    Posts
    530
    Post Likes
    Thanks for sharing looks fun.

  3. #16
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,195
    Post Likes
    Quote Originally Posted by Tech Rob View Post
    Thanks! My motto is "fake it until you make it"!!!

    Lol., cant fake that that too much., good job rob!!
    Rob for president ,,
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  4. #17
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,195
    Post Likes
    So do u use a second chain fall for the shaft to pull the bearing off,(I am assuming)
    To pull off the seal (journal) I only see one.
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  5. #18
    Join Date
    Mar 2007
    Posts
    3,646
    Post Likes
    Thread Starter
    Quote Originally Posted by milkyway View Post
    Lol., cant fake that that too much., good job rob!!
    Rob for president ,,


    Quote Originally Posted by milkyway View Post
    So do u use a second chain fall for the shaft to pull the bearing off,(I am assuming)
    To pull off the seal (journal) I only see one.
    Yes. First chain is to lift the shaft enough so you can remove the bearing support. Once you get it out far enough, you put the dial back on the shaft and put a chain behind the bearing support. Transferring the weight of the shaft from one chain to the other is the trickiest part of the whole job.
    The key to happiness is lower expectations.

    Don't pick the fly crap out of the pepper.

  6. #19
    Join Date
    Mar 2011
    Posts
    1,075
    Post Likes
    Very cool. Those of us DX guys dont get to see too many of these...disassembled anyway!

    Any ideas as to the cause of bearing failure? Oil system blunder?

    Thanks for sharing and keep em comin!

  7. Likes milkyway liked this post
  8. #20
    Join Date
    Mar 2007
    Posts
    3,646
    Post Likes
    Thread Starter
    Name:  262.jpg
Views: 711
Size:  46.5 KB
    Inside the oil tank. Up top is what is commonly called the foam breaker, although that's not really what it does. It's just a mesh screen. On the other side of it a vent line that vents the oil tank to the lowest pressure part of the system. On the back of the tank is the splash guard that covers the oil return from the journal bearing.

    Name:  264.jpg
Views: 720
Size:  40.4 KB
    Here is what the oil pump and motor looks like with the tank head removed.

    Name:  260.jpg
Views: 706
Size:  48.8 KB
    Pulled off the oil line to make sure there were no slugs of sealant or other blockages in the internal oil line since there is no other way to get to it once everything is re-assembled.

    Name:  258.jpg
Views: 690
Size:  41.1 KB
    Here's the gear from the oil pump. The oil pump is a positive displacement gear pump similar to those used in large semi-hermetic reciprocating compressors.

    Name:  267.jpg
Views: 729
Size:  51.9 KB
    This is the end of the oil pump that is directly coupled to the motor. Oil comes in through the top port and is discharged through the copper line attached to the bottom port.
    Last edited by Tech Rob; 11-01-2012 at 08:31 PM.
    The key to happiness is lower expectations.

    Don't pick the fly crap out of the pepper.

  9. #21
    Join Date
    Mar 2007
    Posts
    3,646
    Post Likes
    Thread Starter
    Name:  237.jpg
Views: 739
Size:  40.1 KB
    And here's the view just outside the chiller plant door
    The key to happiness is lower expectations.

    Don't pick the fly crap out of the pepper.

  10. #22
    Join Date
    Mar 2011
    Posts
    1,075
    Post Likes
    Hey Rob can you describe the "air run" with the suction elbow off that you mentioned in your other tear down thread? For those of us who dont know.

    Im assuming it is not to check rotation.

  11. #23
    Join Date
    Mar 2007
    Posts
    3,646
    Post Likes
    Thread Starter
    Sure! An "air run" is when you start the chiller while it is still disassembled to do a balance check and make sure none of the parts interfere with one another once the shaft starts spinning. The process only takes a few minutes. Most chillers have some safeties that need to be defeated before you can do this.

    If you replace any part of the rotating assembly like the motor or impellers, you will need to have it balanced. Typically, if you re-use all of these parts, nothing needs to be changed as far as balance is concerned. It still must be checked, though. It's better to find out while it's all still disassembled, than to find out after it's re-assembled, evacuated, and charged.
    The key to happiness is lower expectations.

    Don't pick the fly crap out of the pepper.

  12. #24
    Join Date
    Mar 2011
    Posts
    1,075
    Post Likes
    I gotcha. That makes sense.

    So you are discharging atmosphere into the condenser? What happens to the motor current during the procedure?

    Do you allow it to come up to speed or just bump the starter?

    I would assume one wouldnt do this on a McQuay.

    That would be scarier than Halloween!

  13. #25
    Join Date
    Mar 2011
    Posts
    1,075
    Post Likes
    Quote Originally Posted by Tech Rob View Post
    Name:  237.jpg
Views: 739
Size:  40.1 KB
    And here's the view just outside the chiller plant door
    Tampa?

    Niiiiiice.

  14. #26
    Join Date
    Jun 2002
    Location
    south jersey
    Posts
    1,887
    Post Likes
    Awsome pics. Love the work you do. Especially love the way you talk us through each pic. Thank you for sharing.
    You need to put the phone down and get back to work!

Page 2 of 6 FirstFirst 123456 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.