10-29-2012, 04:16 PM #14
That is correct.
Each room and each bathroom has one ceiling supply, with the exception of the family room, which has two wall supplies way up high. Open beam ceiling (only iso-board insulation between tongue & groove beams and roof sheathing) in the family room, so these supplies come into the room from the interior wall that abuts the attic space.
See pix. I'm told the new return duct would be beside the ahu... through a new hole to be cut in top of stand... up through the ceiling. There's about 8.5 inches to the right of the ahu for such a duct, since the new ahu will be exactly the same footprint as the old one. Is that wide enough for a jumper duct?
I would certainly expect that to be part of the contractor's job when installing the new ahu/new return duct!
-
10-29-2012, 04:33 PM #15
Professional Member*
- Join Date
- Jul 2006
- Location
- Virginia
- Posts
- 3,705
i would just cut a return in where the coat rack and shoes are , if the supply ducts are sized right and the doors are undercut enough you should be fine
The governent can not give anything to someone that it has not first taken from someone else
-
10-29-2012, 04:41 PM #16
Thanks! That's been the plan from day one until one of the contractors came up with his idea of a return in the ceiling closer to the living areas at the "far end" of the house. Just needed a sanity check to see if having the second return in the foyer was a bad idea.
Is one 20x20 plus one 14x20 (680sq in total) enough return for a 3 ton?
-
10-29-2012, 05:40 PM #17
It will work better than with just one but is not optimal, I use this rule of thumb sometimes total surface area x .8 x 2 so in your case it would be 680x.8x2 =1088cfm which is just over 2.5 tons of air, you need ~1200cfm.
-
10-29-2012, 05:45 PM #18
It shouldn't be a problem to cut the studs and head them off carrying the load of the wall, without looking at it I can't say for sure that wall isn't load bearing but it most likely is not
-
10-29-2012, 06:01 PM #19
Here's what the Florida Building Code says about sizing returns:
SECTION M1403 HEAT PUMP EQUIPMENT
M1403.1 Heat pumps.
The minimum unobstructed total area of the outside and return air ducts or openings to a heat pump shall be not less than 6 square inches per 1,000 Btu/h (13 208 mm2/kW) output rating or as indicated by the conditions of the listing of the heat pump. Electric heat pumps shall conform to UL 1995.
-
10-29-2012, 07:29 PM #20
Professional Member*
- Join Date
- May 2004
- Location
- south louisiana
- Posts
- 2,182
seems to me it would be rather crowded to try to add addtl return duct
to what you have.
it may be best to use other side of r/a wall. 20x20 same as other side so
you only have one size filter to buy. (keep it simple)
cut studs use 2x4 framing of r/a filter grill to carry weight of wall..
once wall is determined not to be load bearing.
make sure that they mastic seal all your duct takeoffs on new trunkline,
and joints & seams of trunkline.
oh and pro's..
wow...anyone notice that furred down hallway??..oh to redo the
ducts and put them ALL inside the fur down...ducts in conditioned space...
wouldn't it be great!
best of luck OP!The cure of the part should not be attempted without the cure of the whole. ~Plato
-
10-29-2012, 08:28 PM #21
I'm not sure what image you're looking at that makes you think the hallway is furred down. All the hallways have 8 ft ceilings with attic directly above, just like all the other 8 ft ceilings in the house. Perhaps the image showing the entry to the family room gives the illusion that the hallway is furred down because the open beam ceiling in that room is about 14 ft high and has no attic above.
-
10-29-2012, 08:37 PM #22
Professional Member*
- Join Date
- Jul 2006
- Location
- Virginia
- Posts
- 3,705
aare you having a media filter installed at the unit ,if so a 20 x20 would be large enough if it does not have a filter in it
The governent can not give anything to someone that it has not first taken from someone else
-
10-29-2012, 08:58 PM #23
No... not enough space above the top of the ahu stand and the ceiling for a media filter. Eight foot ceilings are actually 94 inches above the floor... the top of the stand is 31 inches above the floor... the new ahu itself will be 60 inches, which allows for 3 inches of supply plenum up to ceiling level. The top of the 20x20 filter grille is 26 inches above the floor, so lowering the top of a 31 inch high ahu stand enough to accomodate an 8 inch high media filter cabinet without covering part of the filter grille would be quite a feat!
-