    Need Another Return, But Where?

    Getting close to a decision on equipment and installer to replace my dead 3.5 ton Rheem HP. Leaning heavily toward the 3 ton Greenspeed. Will include some minor reducting to correct the overcooling in the guest bedrooms in the front half of the house closest to the air handler. These ducts currently run directly from the top of the supply plenum to each of two b/r's, the guest bath, and the laundry room (where the air handler sits). Contractor will disconnect these ducts and add a trunk duct to the plenum to a new distribution box where the ducts will be attached (with hand dampers in case further adjustment is needed).

    Also need more return. Existing return filter grille is 20x20 in the hallway near the guest b/r's. It's near the floor and feeds through the wall to the cavity under the air handler stand inside the conditioned laundry room. Initial plan was to add another 20x20 filter grille near the floor feeding through the wall to the same cavity, but around the corner, which puts it in the entry foyer. I now see there may be a better place to put this second return filter grille, but I need some thoughts from you pro's, please.

    Realize my entry foyer and "front" door is actually on the side of my house. The entry foyer opens directly into the atrium area (which is surrounded by sliding glass doors). From the foyer, turn right into the hallway leading to the front of the house with the guest b/r's and guest bath. The tstat and return are in this "guest wing" hallway. From the foyer, turn left to enter the hallway leading to the back of the house, where the main living area is, along with the master b/r and bath.

    Would it be better to put a jumper duct from the cavity under the a/h (run it beside the a/h up through the ceiling), through the attic to a new filter grille in the ceiling in the hallway that leads to the back of the house where the main living area is, along with the master b/r?????? My thinking is that the air supplied to the main living area currently has to move a long, long way to get back to the one return in the hallway at the front of the house. Adding a return around the corner from the existing return wouldn't shorten that distance any.

    Do you need a drawing or a picture?

  2. #2
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,051
    Personally id have air returning inside your house than through a hot attic space.

  3. #3
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,357
    Pictures and/or drawings always help. A proven, sure fire way to increase thread participation on hvac-talk, that's for certain.

    Your existing 20 x 20 return...does it open directly to the cavity beneath the furnace, or must it go up the wall cavity before entering the furnace?
    • Electricity makes refrigeration happen.
    • Refrigeration makes the HVAC psychrometric process happen.
    • HVAC pyschrometrics is what makes indoor human comfort happen...IF the ducts AND the building envelope cooperate.


    A building is NOT beautiful unless it is also comfortable.

  4. #4
    Join Date
    Aug 2012
    Location
    Florida Space Coast
    Posts
    503
    Quote Originally Posted by SBKold View Post
    Personally id have air returning inside your house than through a hot attic space.
    So a return in the foyer is better, even though the foyer has doors to the outside and it's far from the other rooms? The rooms are all open (no doors between) and the mbr door stays open. One contractor suggested the jumper through the attic for the added return. All others never suggested a return duct in the attic, so that's why I ask for advice here.

  5. #5
    Join Date
    Aug 2012
    Location
    Florida Space Coast
    Posts
    503
    Quote Originally Posted by Shophound View Post
    Pictures and/or drawings always help. A proven, sure fire way to increase thread participation on hvac-talk, that's for certain.

    Your existing 20 x 20 return...does it open directly to the cavity beneath the furnace, or must it go up the wall cavity before entering the furnace?
    Opens to the cavity under the a/h. I have a hp only, no furnace (Florida). All supplies are in the attic... nothing in the wall cavities.

  6. #6
    Join Date
    Aug 2012
    Location
    Florida Space Coast
    Posts
    503
    Quote Originally Posted by Shophound View Post
    Pictures and/or drawings always help
    Posting from my Droid, PC problems right now. Will try to post pix soon.

  7. #7
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    7,430
    It's best to keep as much duct out of the attic as possible, also the return nearest the ah will tend to pull most of the air bc air is lazy and will always choose the shortest run. With that said, it would be better to more evenly distribute the return air by having a return on the other side of the house and would help to balance out the hot/cold spots in your home. As long as the contractor uses a high r-value insulation on the new duct and completely seals all the joints it would probably be better for your comfort while not as good for efficiency. Have you looked in to spray foaming your roof deck? Doing that would greatly increase the efficiency of your duct work since it would then be in a semi-conditioned space rather than a sweltering hot attic.

  8. #8
    Join Date
    Aug 2012
    Location
    Florida Space Coast
    Posts
    503
    Quote Originally Posted by jtrammel View Post
    It's best to keep as much duct out of the attic as possible, also the return nearest the ah will tend to pull most of the air bc air is lazy and will always choose the shortest run. With that said, it would be better to more evenly distribute the return air by having a return on the other side of the house and would help to balance out the hot/cold spots in your home. As long as the contractor uses a high r-value insulation on the new duct and completely seals all the joints it would probably be better for your comfort while not as good for efficiency. Have you looked in to spray foaming your roof deck? Doing that would greatly increase the efficiency of your duct work since it would then be in a semi-conditioned space rather than a sweltering hot attic.
    So either way is OK? Comfort in the main living areas/mbr at the back of the house hasn't been a problem with the one 20x20 return. I thought adding a ceiling return near the back would be more efficient. If that's not the case, maybe I should just go with the "easy" way to add a return... through the wall in the foyer to the a/h cavity... provided proximity to outdoors isn't a problem.

    As to foaming the roof deck... I may consider it in the future, after the existing roof is replaced in a few more years. I'd hate to spend money foaming and then find some of my roof sheathing needs to be replaced during the re-roof.

  9. #9
    Join Date
    May 2004
    Location
    south louisiana
    Posts
    3,231
    drawing of house layout & pics will help. please take one showing equipment/platform & return below.

    "Initial plan was to add another 20x20 filter grille near the floor feeding through the wall to the same cavity, but around the corner, which puts it in the entry foyer. "

    not a bad idea, easy enough to do..but.. in the atruim.. in florida..that kind of gives me pause.

    according to what you wrote...and please correct me if I'm wrong..the current r/a
    is on the opposite end of the house from master bedroom & general living area?

    things like jump ducts and/or transfer grills will help to return air from master..
    how many supplies in the master area?

    your ahu closet would have to be pretty big to allow a return duct to be put from
    return on bottom, to besides the equipment..and back into attic to terminate at
    new location. do you have that kind of room?
    will top of this closet be sealed air tight to attic when new trunk/supply plenum is installed?

    depending upon the size of r/a needed..sometimes closets are located centrally and you
    can give up a portion of the closet for r/a. or even a corner of a room..but this would involve
    a good bit of carpentry work.

    post the drawings & pics..we'll take a look.
    it would be nice to keep r/a in conditioned space, but in the big scheme of things..
    putting the supply ducts in conditioned space is the better way. doesn't always
    fit into the overall project scope.

    but jtramel is right..putting ducts in semi conditioned attic (foam sealed attic)
    would be a good savings & improve performance of equipment.

    nice to see someone involved in getting it right.

    best of luck.
    The cure of the part should not be attempted without the cure of the whole. ~Plato

  10. #10
    Join Date
    Aug 2012
    Location
    Florida Space Coast
    Posts
    503
    One more thing to consider.

    May not be able to put a 20x20 filter grille through the wall to the a/h stand cavity from the foyer. The interior width of the cavity on that side is approximately 25 inches. Within that space there are 2 wall studs on 16 inch centers. I'm thinking a filter grille 14" wide by 20" high is about all that will fit without cutting out both wall studs. I'd hate to leave the upper wall in that space supported only by the door frame and the corner support. Refer to pictures to be posted soon.

    20x20 plus 14x20 gives me 680 square inches. I believe that would be plenty for a 3-ton, considering the existing 400 square inches has been in use for over 30 years with a 3.5 ton.

  11. #11
    Join Date
    Aug 2012
    Location
    Florida Space Coast
    Posts
    503
    Can't post all 15 pix at once. Here are the first 9 with 6 more to follow. File names are descriptive.

    Name:  1 - Main Entry Door in Foyer.jpg
Views: 55
Size:  30.3 KBName:  2 - View Atrium From Foyer.jpg
Views: 55
Size:  32.2 KBName:  3 - Hallway to Guest Wing on Right.jpg
Views: 53
Size:  27.0 KBName:  4 - Door to Laundry From Foyer.jpg
Views: 53
Size:  22.5 KBName:  5 - Hallway to Guest Wing (Return).jpg
Views: 54
Size:  16.9 KBName:  6 - Hallway to Guest Wing (T-Stat).jpg
Views: 52
Size:  13.9 KBName:  7 - Hallway to MBR & Main Living Area {Kitchen Entry on Right).jpg
Views: 53
Size:  22.6 KBName:  8 - Kitchen (Glass Doors to Atrium on Right).jpg
Views: 54
Size:  24.9 KBName:  9 - Hallway to Main Living Area (MBR Door on Left).jpg
Views: 52
Size:  15.9 KB

  12. #12
    Join Date
    Aug 2012
    Location
    Florida Space Coast
    Posts
    503
    Here are the last 6 pix.

    Name:  15 - Air Handler Stand in Laundry.jpg
Views: 51
Size:  23.8 KBName:  10 - Hallway Ends at Family Room (Open Beam Ceiling).jpg
Views: 50
Size:  17.8 KBName:  11 - Family Room Ceiling (Dining Entry on Lower Left, Hallway to Foyer on Right).jpg
Views: 49
Size:  17.0 KBName:  12 - Family Room (Add-On Office to Left, Sliding Door to Back Yard on Right).jpg
Views: 52
Size:  17.5 KBName:  13 - Air Handler in Laundry.jpg
Views: 53
Size:  18.3 KBName:  14 - Air Handler & Breaker Box in Laundry.jpg
Views: 56
Size:  23.7 KB

  13. #13
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    7,430
    I don't see enough room to get a return duct up beside the air handler. Regarding a return duct in attic the air would pick up some heat as it traveled through the attic therefore adding to the heat gain of the duct which would slightly increase the temperature of the evaporator coil resulting in less efficiency. Supply ducts in the attic do the same which slightly if well insulated or drastically if not well insulated increase the supply air temperature. It also takes the unit longer to cool down the duct when the unit comes on resulting in decreased efficiency.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event