Thread: Rotating Stall on a York YK

  1. #21
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,625
    Post Likes
    Quote Originally Posted by KnewYork View Post
    If any thread needs to be in the PRO FORUM, this is it. There is no way a technical conversation as deep as is warranted here should be in the open forum.
    I agree. Sounds like deja vu. But I don't think it'll get much deeper. The customer didn't need a chiller of the size they have, and they need to turn the one off that they bought. Thousand different ways to do that, but instead of turning it off the chillers a piece of crap because the compressor engineer at York doesn't agree with the guy that's been hired to work on the chiller.

    MFT: I'm sorry as I can be if you don't like what's being said, but I had a 50° delta T (90° to 40°), 5 pass, 600TR PACKAGE chiller one time that ran during the winters with 43° entering water from the settling ponds at the mill. Chiller logged around 28,500 starts in 6 years (2300 volt A/L start). Four motor rebuilds for busted rotor bars before the thing finally extruded the front HS bearings out of it. Rebuilt the two sitting in the same plant on the same process for the same reasons, first one was replaced because of the halogen fire when the impeller drug on the diffuser. It wasn't the chillers fault...

  2. #22
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,042
    Post Likes
    Coming across a poor application, that has frustrated the customer and given the manufacturer a bad reputation (in the customer's eye), is an opportunity for a tech to really shine. They are not to be squandered....

  3. #23
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,625
    Post Likes
    Quote Originally Posted by Nuclrchiller View Post
    Coming across a poor application, that has frustrated the customer and given the manufacturer a bad reputation (in the customer's eye), is an opportunity for a tech to really shine. They are not to be squandered....
    Hear, hear.....

  4. #24
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    Quote Originally Posted by man from trane View Post
    So I guess the consensus is they're just going to have to shut the machines off when there's no load. So why in the world did York even provide a Disable Setpoint?! What could this possibly be used for if the machine can never reach setpoint - 1°? The only thing I can think is if you have multiple chillers on the same loop and another chiller has a lower LWT setpoint. But I only have one chiller (for now, they're going to add another) so I'm screwed.

    So, how long can this thing surge like a locomotive before the compressor is toast?
    No load is no load is no load and no chiller no matter how many bells and whistles you put on it or into the programme that controls it can change that . SHUT THE FREAKIN THING OFF !!!!!!!!!!....or generate sufficient load to keep it happy .

    As for how long it will run before self distruction ......... is that really relevant ???
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  5. #25
    Join Date
    Apr 2012
    Location
    Louisiana
    Posts
    929
    Post Likes
    Could cycle it on return temp.

  6. #26
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Quote Originally Posted by Sicofthis View Post
    Could cycle it on return temp.
    Not a very good idea when there is no load. The thing will cycle itself to death as pointed out earlier.

  7. #27
    Join Date
    Apr 2012
    Location
    Louisiana
    Posts
    929
    Post Likes
    Quote Originally Posted by KnewYork View Post
    Not a very good idea when there is no load. The thing will cycle itself to death as pointed out earlier.
    Op said it spent 30 mins at 32 degree return with machine off. If that's true why couldn't you shut down at 32 an bring it on at 40 or more? Wouldnt that be better than leaving it on with no load? Im not very experenced with centrifugals. Op hasn't stated how critical supply temp is.

  8. #28
    Join Date
    Jun 2006
    Location
    Omaha, Nebraska
    Posts
    882
    Post Likes
    Thread Starter
    In the late '90s I ran a plant with (2) 750 ton Trane Centrivacs. Sometimes the load would drop off when the outside temp fell suddenly and the AHU's started running mixed air. I'd sit there in the engineering office and hear the lead machine cycle off. If the LWT came up after a while it would restart. What a concept. Those chillers had no bells or whistles. No Variable Speed Drive, no Solid State Starter, no Hot Gas Bypass, no Variable Geometry Diffusers, no Optiview, actually a very simple design. They're still running to this day, years later and the only time I ever heard one surge was if the condenser water went above 86°F. Then all I had to do was raise the CW Setpoint a bit. I never even knew what a Rotating Stall was until I encountered these YK machines.

    Maybe the YK is a great machine. Maybe they are misapplied at this plant. I don't work on centrifugals often, but I would think in 20+ years I would have encountered this problem on other machines but I have not.

    No one ever answered my question about why the machine has a Disable Setpoint if it is incapable of making chilled water colder than the setpoint. Why not just have a single LWT setpoint and leave it at that? It never cycles off no matter what. And since my name is on the log it is very relevant to me if a 6 month old compressor shells out.

  9. #29
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Quote Originally Posted by man from trane
    No one ever answered my question about why the machine has a Disable Setpoint if it is incapable of making chilled water colder than the setpoint. Why not just have a single LWT setpoint and leave it at that? It never cycles off no matter what.
    The chiller you have was selected by someone to perform a certain function. We don't know how or why it was selected. I will guarantee you that any of the former York (or present JCI) guys who frequent this site could get that machine to behave (and shut off). A thorough understanding of the various components and programming of the Optiview panel come into play when a machine isn't performing. You aren't dealing with a standard comfort cooling machine like those old CVHEs. Yorks will cycle just like those CVHEs when applied in a comfort cooling application. You have a more complex system and the system (outside the chiller) isn't doing what its designed to do and you're blaming the chiller. You even stated in your original post that they are having problems with their process.

  10. #30
    Join Date
    Jun 2006
    Location
    Omaha, Nebraska
    Posts
    882
    Post Likes
    Thread Starter
    I would like to see the JCI tech get it to cycle off. Are there some hidden parameters I can't see from service mode? Even the service manual says it's doing what it's supposed to by not opening the HGB unless there's a surge condition. JCI won't be coming back here unless there is a major issue that we can't handle. That's why I would like to be able to correct this without getting them involved.

    In another part of the building there are (2) smaller YK chillers used for HVAC that also do not cycle off. But they will sit and surge rather than stall.

  11. #31
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,625
    Post Likes
    Quote Originally Posted by man from trane View Post
    I would like to see the JCI tech get it to cycle off. Are there some hidden parameters I can't see from service mode? Even the service manual says it's doing what it's supposed to by not opening the HGB unless there's a surge condition. JCI won't be coming back here unless there is a major issue that we can't handle. That's why I would like to be able to correct this without getting them involved.

    In another part of the building there are (2) smaller YK chillers used for HVAC that also do not cycle off. But they will sit and surge rather than stall.
    I'm not with York anymore (never did consider myself to be with jci), but if you'll get me a PO I'll come to Omaha and show you how. I'm not cheap, but I'm easy

  12. #32
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,752
    Post Likes
    This entire discussion is explained in great detail in IOM 160.54-m1 this thread should be in the pro forum.
    A mind is like a parachute. It doesn't work if it is not open.

    The best part of going to work is coming back home at the end of the day.

    Hard work spotlights the character of people: some turn up their sleeves, some turn up their noses, and some don't turn up at all.

  13. #33
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by klove View Post
    I'm not with York anymore (never did consider myself to be with jci), but if you'll get me a PO I'll come to Omaha and show you how. I'm not cheap, but I'm easy
    i am 2 hours from omaha...1:30 if there aren't any cops!
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  14. #34
    Join Date
    Jun 2006
    Location
    Omaha, Nebraska
    Posts
    882
    Post Likes
    Thread Starter
    That might not be out of the question!

  15. #35
    Join Date
    Jun 2012
    Location
    so cal
    Posts
    22
    Post Likes
    hot gas will open up at 1 degree below leaving chilled water set point unless you set it to 2 then it will be 2 below set point and so on....

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •