    Carrier 355MAV with Evolution Control Help

    Ran a call today for a customer that has a Carrier 355MAV furnace with a Evolution control stat.

    Furnace: 355MAV042080
    Thermostat: SYSTXBBUID01



    Here's the situation:

    Evolution control is showing a variety of errors (listed in the pics below)
    I am the third tech to take a look into this
    A week ago an April Aire #700 was installed and a clean/inspection was performed, cleaned burners, flame rod, condensate trap.
    Ever since this furnace has been throwing codes daily

    Here are the codes I saw this afternoon:

    Name:  photo3-2.jpg
Views: 1223
Size:  28.1 KB
    Name:  photo2-1.jpg
Views: 1415
Size:  30.0 KB
    Name:  photo.jpg
Views: 1219
Size:  30.5 KB

    The code 33 and 34 is what I am having trouble with, not sure if they are A/C related or heat related? Can anyone tell me what those faults are?

    I also checked the humidifier wiring and they have the solenoid connected to the HUM and COM terminals on the furnace control board, this appears right.

    Any help is much appreciated.
    UA LU189

  2. #2
    Join Date
    Aug 2012
    Location
    MN
    Posts
    149
    Post Likes
    Bypass humidifiers are wired that way on the furnace, the Evolution will energize hum during a call for humidification and can be set for heat only or with fan. With a bypass humidifier installed go into advanced settings and turn low heat rise on it increases air flow, which you want to do now that your return air is warmer. You can also go into furnace set up and change air flow from comfort to efficiency increasing air flow even more this should take care of the limit fault(33).
    34 is ignition proving fault usually dirty flame sensor but could be rough ignition or low inlet gas pressure, 32 can also be low gas pressure if its lp with a lgps switch which is in series with your pressure switches.

  3. #3
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    2,759
    Post Likes
    Thread Starter
    Thank you PCP, I will be back at the job tomorrow to do as you advised.

    UA LU189

  4. #4
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    These furnaces always have trouble. You need to increase airflow. Also should setup low, med, and hi fire with a combustion analyzer. Years ago I always had errors with ignition, limits, etc... Until I started tuning with a CA. With a 90% furnace, you need 150cfm per 10,000 input btus

  5. #5
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    2,759
    Post Likes
    Thread Starter
    Quote Originally Posted by gravity View Post
    These furnaces always have trouble. You need to increase airflow. Also should setup low, med, and hi fire with a combustion analyzer. Years ago I always had errors with ignition, limits, etc... Until I started tuning with a CA. With a 90% furnace, you need 150cfm per 10,000 input btus
    Thanks Gravity. I returned to the job today and increased the airflow per PCP's instructions. Advised the customer to keep and eye on things and let me know.
    UA LU189

  6. #6
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    You also need to watch out for the venting.

    If your flue is too small or too long of a run, it may work but it will burn horrible.

    No way to tell this unless using a combustion analyzer.

    Just make sure the venting is by the book and you use the restrictor plates in the intake properly

  7. #7
    Join Date
    Jun 2012
    Location
    nampa idaho
    Posts
    66
    Post Likes
    That's funny my last call today was one of these, code 45 on a heat pump, had to replace the board on the heat pimp

  8. #8
    Join Date
    Jun 2012
    Location
    nampa idaho
    Posts
    66
    Post Likes
    The fn is for the furnace

  9. #9
    Join Date
    Jun 2012
    Location
    West
    Posts
    60
    Post Likes
    Airflow is a good thing to check, if you get a call back confirm heat rise, gas pressure and if you have an N-coil for the evap that doesn't match the furnace casing size wise make sure its positioned correctly-N coil overhanging the wrong side alone can cause limit trips

  10. #10
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    2,759
    Post Likes
    Thread Starter
    To follow up:

    I went back Monday and changed the settings per PCP's advice in post #2. It's now Wednesday and there hasn't been a single trip. Turns out the LPS and ignition issues were caused by the tech checking the safeties during the inspection. The date and time were not set properly on the stat.

    So far so good. Thanks guys.
    UA LU189

  11. #11
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    Thanks for the update.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •