    Jan 2010
    Toronto,Ontario Canada
    Walk-in freeer Compressor blowing start caps
    walk in freezer having issues
    Some other company converted the old system from a water cooled condenser to a air cooled condenser which is still located inside the restaurant. approx 4 yrs old
    My buddy from work gets called in saying their freezer down, he found a bad start cap, so he replaced it and it worked fine. A few days later i get called back to this site and same thing. Top of the compressor is extremely hot and it wont start. Investiated and discovered start capibilties gone again. start cap is blown. I replaced the start cap run cap and the potential relay (took down the compressor info and got the correct parts for that compressor) Also cleaned the condenser for good measures. incase its getting too high head.
    Replaced the parts checked pressures and amps everthing is fine. I got advised by my boss that the compressor is on its way out and to let the manegers know about issue. Now today i get called from my boss that the system is down again. Same issue, but this time he went there to talk to maneger. we are looking to replace the compressor in a few days or even installing a condenser for the roof due to the temperature inside the restaurant.
    Just curious is this common thing to happen that this compressor is having a hard time starting and blowing the starting components. is this a good sign of the compressor being bad? Thinking that the people that put in this system didnt do their job of doing a proper vacuum or dirty refrigerant. Is there any other issues that may cause this to fail?
    Just wanting some input much appreciated
    Get er Done!
    Do what has to be done
    when it has to be done
    as well as it has to be done
    And doing it all the time.
    Dec 2003
    Citrus County, Florida
    Compressor bearings could be dragging. Possibly compressor shuts down when satisfied; sometimes armature is in a good position to start and sometimes not.
    Doug
    Southeastern Pa
    It could be that if the compressor is not running correctly (too slowly) the potential relay is keeping the start cap in the circuit. That would kill the cap.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Jan 2006
    DFW Metroplex
    The only things that come directly to mind that would continually take out a start cap are
    (1) Improper part/application (based on the info in your OP though, we can most likely rule that out).
    (2) Current/potential relay hanging up (again, being that you changed the relay this would be highly unlikely as well).
    (3) Improper voltage supplied to system (is the pump getting a full 120/240V? If not, this could very well be the problem).
    (4) Excessive short cycling (any more than ~10 cycles per hour could cause premature start cap failure).
    (5) Compressor mechanical wear (See Gunslinger's post).
    Personally, I would say this isn't necessarily a 'common' problem as oftentimes mechanical wear will completely lock the pump up or burn out the start winding - and prolonged low voltage/short cycling will usually cause a catastrophic electrical failure in the motor (start) winding long before taking out several start capacitors in succession.
    Just shooting from the hip, if your voltage is ok, I'd tend to be of the same opinion as your boss at this point.
    "The problem is the average person isnt tuned in to lifelong learning, or going to seminars and so forth. If the information is not on television, and its not in the movies they watch, and its not in the few books that they buy, they dont get it" - Jack Canfield
    Nov 2010
    Does it have a CPR valve? An incorrectly adjusted or faulty/nonexistent crankcase pressure regulator valve can cause the same symptom. Excessive crankcase pressure can cause a hard start condition and subsequently kill your start capacitor.
    Sent from my MB886 using Tapatalk 2
    Jan 2010
    thank you all for the responces. this just makes a better tech. i will do a better look the next time i run into a problem similair to this one. all info is much appreciated.
    Get er Done!
    Jul 2012
    Kansas
    LL solenoid may be leaking through after the box temp is satisfied, causing short cycling.
    Mar 2009
    Mid-Mo
    I was thinking it might be starting flooded....
    Feb 2007
    Georgia
    That CPR is a big issue if it occurs after defrost. You can actually observe this after defrost it will literally bring start circuit in and out many times. K body (small air cooled) Copelands are especially prone to this.
    Failure of the defrost termination circuit will aggravate the problem as the evap will overheat during defrost
    Quote Originally Posted by zxcb View Post
    ran across one last week short cycling , I thought it might be the LL solenoid , but turned out was a reed valve was leaking and wouldnt stay pumped down more than 20 seconds .... got a new compressor
    Dec 2010
    Savannah Ga.
    Check all switches in the control circuit to the contactor coil. Usually when we run into this it is either short cycling as already stated, or a problem with a pressure switch where the switch instead of snapping positively open and remaining open, will open/close/open/close/open/ close repeatedly until something blows....start capacitor.
    Southeastern Pa
    Quote Originally Posted by icexprt View Post
    Not just pressure switches, either. Recently, I had an ice machine condenser that locked out on shutdown. I replaced the low pressure switch because of the heavy use, but it was poor continuity of the contactor that was the power source for the pressure switches in the condensing unit, and when the contactor chattered it pulled down the voltage in the 208 volt safety circuit, which in turn, meant a loss of coil voltage in the contactor. New switch, new contactor, done deal.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Apr 2012
    Louisiana
    I concur.
    I'd bet money something is causing your compressor to short cycle or contacts chatter.
    You did not say if you checked voltage at the compressor or if starting and running amps are good.
    Edit: reread and found where you said amps were okay.