    Metasys VMA not taking Set only Override

    Hi,

    Just switched over some 100 VMA's to N4 and for some reason the setpoints only take when overriding it. Set just sits there and doesn't update.



    Sent from my iPhone using Tapatalk
    Knowledge is money - Ignorance is expensive!!

  2. #2
    Join Date
    Feb 2009
    Location
    South Florida
    Posts
    51
    Post Likes
    It appears that you are dealing with n2. I don't believe that the default value priority used in bacnet will work in this application. Write at a different priority and I suspect you won't have any issues.

  3. #3
    Join Date
    Mar 2009
    Location
    Several Miles from Sane
    Posts
    1,712
    Post Likes
    vaultein,
    If this is an FX-60/70/80 you should select the "Slave Policy" for any point that needs persistent write/rewrite operation. Is it an FX JACE ?

    I am not sure but you may be able to un-hide the "Setpoint" on the slotsheet in N4 (FX-14). I do not recommend it as that function writes to EEPROM. Changing the tuning policy should solve your problem.
    If sense were so common everyone would have it !

    Any advice provided is worth exactly what you paid for it, not a penny more not, a penny less !!

  4. Likes WillyTech liked this post
  5. #4
    Join Date
    Jul 2009
    Location
    Wa
    Posts
    229
    Post Likes
    Cagey is right. The tuning policy is your answer.