    I have a steamer that the hotel has and it is a 208 single phase or 208 three phase.(not hooked up) My problem is I only have 480 three phase near the steamer. All the wiring is under the floor and cannot be rewired or pulled for new. Isnt there a step down transformer for this situation?

  2. #2
    Join Date
    May 2004
    Posts
    14,135
    Post Likes
    Using a step down is a good idea if it wasn't for the high amp draw. It may be cheaper to change the elememts to 480 and step down the controls.



  3. #3
    Join Date
    Jun 2006
    Location
    Las Vegas,NV
    Posts
    116
    Post Likes
    I agree

  4. #4
    Join Date
    Jul 2005
    Posts
    38
    Post Likes
    Ditto.