Results 1 to 13 of 25
Thread: rooftop charging in winter?
-
10-26-2012, 07:02 PM #1
Professional Member
- Join Date
- Jul 2012
- Location
- Peace River, Alberta, Canada
- Posts
- 46
rooftop charging in winter?
any good tips on how to charge a RTU during winter? tried yesterday and set off the freeze stat...
-
10-26-2012, 07:16 PM #2
-
10-26-2012, 07:18 PM #3
Hi Nrmika,
You must weigh the refrigerant charge into the RTU.
Keep warm thoughts.
Good luck,
AllenUA Local 602
A man who says that he can't learn anything in a class is exactly right.
-
10-26-2012, 07:28 PM #4
Professional Member
- Join Date
- May 2002
- Location
- evansville indiana
- Posts
- 892
Yep ,easiest way is to weigh it in ,even if you have to recover the remaining charge (if any )
On a split you can calculate using equipment literature.
Or you can guess,using your tools ,and probably get pretty close, but that only counts in horshoes and hand grenadesmikeacman
-
10-26-2012, 07:31 PM #5
Professional Member
- Join Date
- Jul 2012
- Location
- Peace River, Alberta, Canada
- Posts
- 46
I was weighing in but it set off the freezestat. Feathering to fast?
-
10-26-2012, 07:33 PM #6
Professional Member
- Join Date
- Feb 2007
- Location
- Georgia
- Posts
- 116
You do have to weigh it in
However you may have to block condenser to keep head up so the suction will stay up so you can get system to take charge without it cycling on freeze stat.
Using cardboard to block entering air to the condenser usually works great
-
10-26-2012, 07:49 PM #7
Professional Member
- Join Date
- May 2002
- Location
- evansville indiana
- Posts
- 892
To add ,I use my recovery machine to recharge units . I can weigh it all in before I even start the unit up....
After all ,its a refrigerant pump....mikeacman
-
10-26-2012, 08:07 PM #8
Professional Member*
- Join Date
- Apr 2011
- Location
- Coastal Maine
- Posts
- 573
Mike is right. That is how we do it in cold weather. Awful hard to create enough head even with blankets and cardboard when it is below zero. Which means that we wouldn't be able to work on them all winter. So we put the weighed charge in with the recovery machine, then start it up. Never fails, we always have to go back in the summer and trim the charge or adjust the TXV, but it gets us close. Sucks doing AC work when it is below zero.
-
10-26-2012, 08:42 PM #9
Professional Member
- Join Date
- Feb 2007
- Location
- Georgia
- Posts
- 116
Wow down here 20f is cold
I say let's drink some coffee and charge it next summer
That trick is a first for me I sure hope I never have to use it
-
10-27-2012, 12:23 PM #10
Professional Member
- Join Date
- Sep 2006
- Location
- Ohio
- Posts
- 354
If the system was evacuated to 500 microns or lower, You should be able to get most of the charge in without even starting the unit. I will use a torch to warm the refrigerant drum if it won't pull in the entire charge by itself. You could also use a heat gun if you have one, but a MAP gas torch works great.
-
10-27-2012, 12:36 PM #11
Professional Member
- Join Date
- May 2002
- Location
- evansville indiana
- Posts
- 892
-
10-27-2012, 02:49 PM #12
Sell them an economizer?
-
10-28-2012, 05:47 PM #13
Professional Member
- Join Date
- Sep 2006
- Location
- Ohio
- Posts
- 354


Reply With Quote