    RUUD UPRL-JEC HEAT PUMP ICING UP

    We had a new RUUD communicating system (UPRL-JEC 3 ton heat pump w/ RHPL-HM3621JC air handler) installed a couple of years ago. It has worked fine until this cold season. On a cold night, ice builds up around the upper half & top of the outside unit. It sounds like it is going into a defrost cycle, but the ice remains until the outside temperature rises above freezing the next day.The serviceman has been a couple of times to check it, but can find nothing wrong. He said it was not low in refrigerant. Any suggestions on what the problem could be??

  2. #2
    Join Date
    Aug 2012
    Location
    willowick ,oh
    Posts
    261
    Post Likes
    Get a second opinion. You could have a distribution issue with the refrigerant or a check valve not seating. Im not going into detail because i am not on site. Call a pro and make them explain why it is doing what its doing.Could be a few things causing it.

  3. #3
    Join Date
    Jan 2008
    Location
    Texas
    Posts
    4,126
    Post Likes
    Could be od stat, timer setting, or other. As said you need another opinion.

  4. #4
    Join Date
    Oct 2009
    Posts
    89
    Post Likes
    Thread Starter
    I will try and get a 2nd opinion, but I live in a rural area and there are not a lot of heating & air contractors in my city.

  5. #5
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    39,246
    Post Likes
    We had a RPQL that had a STRANGE issue. It would go into defrost but the board wouldn't stop the outdoor fan, so ice built up. Local tech support looked at it and reported to the factory. We ended up having to upgrade this heat pump to a new type of board. If you hear a defrost where the reversing valve makes the woosh sound, see if the outdoor fan stops during the defrost.

  6. #6
    Join Date
    Oct 2009
    Posts
    89
    Post Likes
    Thread Starter
    OK thanks BaldLoonie for the tip!! I will see if the fan stops when I hear it go into the defrost cycle.

  7. #7
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,671
    Post Likes

  8. #8
    Join Date
    Oct 2009
    Posts
    89
    Post Likes
    Thread Starter
    I gave the contractor the information about the outdoor fan could be the problem due running during the defrost cycle. He was happy I gave him this information so he called the Ruud Distributor and they discussed what was happening. He changed out the board last week, but today it is really cold outside and I noticed ice was building up around the top half of the unit again. I called the contractor back and left a message. I will verify with him what kind of board he replaced it with, but I noticed in the post you upgraded the heat pump with a new type of board. What type of new board did you upgrade it too?? I want to give him this information so he can discuss it with the RUUD Distributor. I read the AOP forum rules so hopefully the post will be in accordance with the rules. I definitely am not a DIY type of person, but my contractor really appreciates the information.