Results 14 to 26 of 33
Thread: Changeing out 40 ton condensers
-
10-26-2012, 09:32 PM #14
Regular Guest
- Join Date
- Oct 2012
- Location
- San Diego CA.
- Posts
- 19
Thanks for all the advise. I did cut out all the low spots and blew a rag- plug thru the line set. Started one side of one unit today and low and behold no problems. Will be hopefully start other circuits tommorow. I pulled a deep vac 4 times and introduced 410 each time to grab any moisture. Oil at compressers looks good and I am getting 40 degrees at evap coil.
-
10-28-2012, 11:01 PM #15
Professional Member
- Join Date
- Nov 2005
- Posts
- 1,311
I have been down this road and I am still on it. I am in the process of replacing both compressors. Is it a Trane?
I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!
-
10-29-2012, 12:17 AM #16
Regular Guest
- Join Date
- Oct 2012
- Location
- San Diego CA.
- Posts
- 19
Yes and I plan on changeling out compressor oil a couple of times just to make sure it's more poly than mineral
-
10-29-2012, 06:39 PM #17
Professional Member
- Join Date
- May 2002
- Location
- evansville indiana
- Posts
- 892
-
10-29-2012, 08:23 PM #18
Regular Guest
- Join Date
- Oct 2012
- Location
- San Diego CA.
- Posts
- 19
I will be picking one up as you suggested
I definetly see a diferance in the oil and have ordered poly oil in to replace . I just can't believe how expensive it is
Thanks
-
10-29-2012, 08:25 PM #19
Regular Guest
- Join Date
- Oct 2012
- Location
- San Diego CA.
- Posts
- 19
It is a Trane and new oil is 4 days out. I hope the compressors last that long there not acting up or over heating I just don't like the look of the oil thru the sight glass
-
10-29-2012, 08:32 PM #20
Regular Guest
- Join Date
- Oct 2012
- Location
- San Diego CA.
- Posts
- 19
Allstar08,
What were the problems you that you were having and how many times did you change the oil
I noticed after the first day we had to drain some of the oil because the compressors were getting to full
-
10-29-2012, 08:47 PM #21
Professional Member
- Join Date
- May 2002
- Location
- evansville indiana
- Posts
- 892
im not the OP ....but I had a run in with mixed oil....
I had a factory ordered water cooled (condensor ,air over evap) split that was built to run on R134A and carrier filled the comps with mineral oil .... I spent a couple days and if I remember went thru 20 gallons (for two 06E's) of oil before I was under 5% mineral to poe ....
im thinking around 5 changes per compressor ....
134 because it was a refrigerator factory and they wanted a cooling system for their offices that ran on 134A,just like their product
my experience was the mineral tended to lay out in the system and as you got more poe in it all started coming back at a rate that I had to babysit it .... at first the oil just left and did not come back . I had a gut feeling before I started it that it was wrong but was shown it was ordered for 134A service . My gut was right.
.
Without an oil refrac I would have been guessing ....that unit has been running close to ten years now with no compressor failures....mikeacman
-
10-29-2012, 09:11 PM #22
Regular Guest
- Join Date
- Oct 2012
- Location
- San Diego CA.
- Posts
- 19
Thanks for the info
I flushed the holy crap out of the system but there is no way to get all the mineral oil out
I hope the compressor collects most of it and it doesn't take to many changes
I get the two oils don't mix but I wouldn't think it would damage the compressors to bad scrolls are fairly forgiving ( I pray )
-
10-29-2012, 09:31 PM #23
Professional Member
- Join Date
- May 2002
- Location
- evansville indiana
- Posts
- 892
I started with 100% wrong oil ,,,my case was extreme ,,,being burned by that I just won't guess anymore ....sounds like you have a handle on it ...
mikeacman
-
10-29-2012, 09:44 PM #24
i know that you are just asking about oil changes, but you did change out the compressors too...right? txv's? you might consider running for the border when this is done. change your phone number. change the company name. mother nature doesn't care if your budget can't handle it. r22 and r410a are 2 very different refrigerants and they require the proper engineering and design to make them work. you will probably be changing out the evaporators before too long.
not that it has to do with your original question, but why did the old compressors not last long? if it wasn't corrected, then, you should know that the new compressors are more expensive to replace than the old compressors were.The weak aren't destroyed by the strong.
The weak are destroyed by the under-estimated.
I know a famous song that ends in 'my nose'. The artist is dead. Know who?
-
10-29-2012, 09:51 PM #25
Regular Guest
- Join Date
- Oct 2012
- Location
- San Diego CA.
- Posts
- 19
Yes I changed out all the goodies and rerouted the line set to get rid of the traps and low spots
Trane confirmed that the existing coil could handle 410
The existing unit killed quite a few compressors and it looks like it was because the way it was set up it kept lugging the compressors with oil
I'm not using the hot gas bypas but frost stats instead and so far were not slugging
-
10-29-2012, 09:53 PM #26
Regular Guest
- Join Date
- Oct 2012
- Location
- San Diego CA.
- Posts
- 19
Thanks for the info