Results 14 to 26 of 30
Thread: Charging to full sight glass?
-
10-25-2012, 07:45 PM #14
Regular Guest
- Join Date
- Apr 2010
- Posts
- 75
This looks like my answer. My receiver is the size of the refrigerant tank. There's not enough info on the condensing unit to get an accurate manufacturer - and the charge amount was written in sharpie, so it's not the first time its been serviced. For all I know, the 33lb could be low. It has a headmaster, and the rooftop temp at the time was 72. I wish I could've gotten the head pressure, but by then the guy had pulled the hi side off and was charging low side. Yeah, I shoulda put a high side gauge on and confirmed pressures, but by then we were wrapping up. Anyways, today I called and they told me the unit was still down in temp, but one these days I'm gonna go back and double check everything.
Lesson learned - do your own follow ups, and if you can't, make sure the guy following up is doing it right.
-
10-25-2012, 08:12 PM #15
-
10-25-2012, 08:16 PM #16
http://sporlanonline.com/90-30-1_072012.pdf
I use this for charging systems with a headmaster control.
If you've got a receiver in the system, charging to subcooling is a no-no. It won't work for you.
-
10-25-2012, 08:17 PM #17
-
10-25-2012, 10:06 PM #18
-
10-25-2012, 11:03 PM #19
Professional Member
- Join Date
- Oct 2012
- Location
- CA
- Posts
- 209
One should never use subcooling with a receiver in a system ? I did not know that .
-
10-25-2012, 11:12 PM #20
I usually just add refrigerant until the compressor starts to rumble. That way I know I'm slightly over charged. Then block the condenser and let the auto reset pressure relief pop off, once it resets, your system should be correctly charged.
-
10-26-2012, 09:22 AM #21
-
10-26-2012, 05:32 PM #22
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 914
-
10-26-2012, 05:34 PM #23
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 914
-
10-26-2012, 05:40 PM #24
This reminds me of a dude that used to work where I do before I got there. The old supervisor tells a story of him soon a tune up on a 5 ton rheem split where he knuckled in the contactor and was watching the suction pressure. Of course it didn't go up so he adds refer. Keeps adding it until the compressor locks up, somewhere in the neighborhood of 30 lbs. Come to find out he didn't turn the air handler on. Lol.
-
10-28-2012, 01:55 AM #25
In looking at the above figure, the following may explain why you were seeing bubbles in the sight glass.
As the system head pressure falls below the set point of the headmaster, the valve starts to modulate - closing off port C and opening port R by the same ratio. This results in refrigerant backing up in the condenser as discharge gas begins diverting directly into the receiver.
Conversely, as the head pressure hits the set point of the headmaster, the valve starts to modulate once again - opening port C and closing port R by the same ratio....resulting in increased flow of refrigerant through the condenser into the receiver and restricting discharge gas from dumping directly into the receiver.
More than likely while you were adding refrigerant to the system, the discharge pressure temporarily exceeded the headmaster set point and therefore refrigerant was not allowed to stack in the condenser - so your system was sufficiently charged.....briefly.
Once you stopped adding refrigerant and the system was allowed to stabilize, the head pressure most likely dropped below the headmaster set point and refrigerant started stacking up in the condenser - and where you barely had enough refrigerant in the system before, now there simply isn't enough of a charge to both stack in the condenser and maintain a liquid level in the receiver.
Start adding refrigerant again and the cycle repeats.....until such time there is enough of a charge to allow the headmaster to do its job and form a liquid seal at the outlet of the receiver.
If you spend some time studying the figure and reflecting on how subcooling is derived, it should also become readily apparent as to why charging by subcooling simply is not an effective way to determine an acceptable system refrigerant charge.
I haven't clicked on JPSmith's link, but I would imagine he is directing you to Sporlan's step-by-step procedure for properly charging a system such as the one you are working on."The problem is the average person isn’t tuned in to lifelong learning, or going to seminars and so forth. If the information is not on television, and it’s not in the movies they watch, and it’s not in the few books that they buy, they don’t get it" - Jack Canfield
-
10-28-2012, 09:44 AM #26




Reply With Quote