Ok, ran into an odd one. Typical call for a large WIF down. On roof, sight glass barely showing any refrigerant. Electronic leak check, found two leaks: One at low pressure control, other in suction line vibration absorber. Since it was in a major downpour, I gassed up for now to a full sight glass. The unit is listed at 33lbs of 404. I only had to add 5 lbs and told them I'd return.
Now, I had soaped up the vib absorber and it bubbled pretty good, but I figured it'll hold for a while until I return. But they called back the next day saying the unit was down already. Ok, I figure the vib absorber was probably leaking worse when the unit was running (checked while it was idle due to the condenser fan blowing all over). Another tech returns to complete the job, and I wind up meeting him on site after he's 90% done. He pumped down unit, changed drier, changed vib absorber and pressure control. He was in the process of adding gas. Sight glass clear after 6 lbs. Unit coming down in temp. Time to wrap up.
Then the sight glass started bubbling again. I figure the evap fans just came on, so lets add a bit more. Another 2 lbs. Ran clear - then about 10 minutes later, just as we were wrapping up AGAIN, started bubbling again. Ok, add another 2 lbs. Ran clear again, and slowly started bubbling AGAIN. So we started doing a more thorough leak check, using two electronic leak detectors and ran across every inch of tubing. I figure a leak that big should be blowing our hair back. But found nothing. It seemed we had to keep adding gas to clear the sight glass. After about an hour, and another 6 lbs, it finally started to stay clear.
Is this unusual, or common for a system with such a large receiver? Unit does have headmaster, so its possible that wasn't opening as well.
-
10-25-2012, 05:54 AM #2
You need to look at how your head pressure is controlled. What was the temperature where the condenser is located.
Aire Serv of SW Connecticut- Gas heat, dual fuel and central a/c systems installed and serviced
-
10-25-2012, 06:09 AM #3
The txv could have been opening and closing, I would verify that the txv is the correct size and the bulb is mounted correctly. Also, with a headmaster. You will need to add additional refrigerant after the sight glass is clear. I believe its an additional 20%, but I would check with the condenser manufacture.
-
10-25-2012, 07:50 AM #4
Professional Member*
- Join Date
- Aug 2012
- Location
- willowick ,oh
- Posts
- 163
You said its a 33 lb system. If it has a headmaster you were probably just low on refrig. It depends on the temp outside tho. Need all of the numbers to be sure. , sc idt odt delta, pressures. things that matter. You could have a 15 lb reciever on that pig or bigger. Your headmaster is gonna compensate for a low charge until you have some juice in the reciever.
-
10-25-2012, 11:21 AM #5
Your still low. Like already pointed out you should have a good sized receiver. If its warm out your glass will fill but receiver will be empty so when headmaster starts throttling all your liquid gets stacked in cond coil and glass will start flashing. You can, and I would pull the charge and weigh it back in. Or keep guessing at it and give yourself grey hair. That's where mine came from.
-
10-25-2012, 12:05 PM #6
Professional Member*
- Join Date
- Aug 2012
- Location
- willowick ,oh
- Posts
- 163
-
10-25-2012, 12:47 PM #7
I haven't seen a nameplate charge on any of our refrigeration units. Agreed with everyone else that it sounds like you're still short on happy juice.
-
10-25-2012, 02:29 PM #8
-
10-25-2012, 06:16 PM #9
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 904
Yep add the flooding charge after the glass is full AND system is almost at set point.
Your evap coil will use much more refrigerant as it get cold, as less refrigerant is boil off and the coil is more flooded..... Unless your TXV is grossly oversized.
-
10-25-2012, 06:43 PM #10
Forget the sightglass, charge by subcooling it's to only way to tell if the system is fully charged.
I use the sight glass for the moisture indication only.
-
10-25-2012, 07:08 PM #11
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 904
-
10-25-2012, 07:24 PM #12
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 904
I would agree with you on a cap tube unit or a system with no receiver subcooling needs to be checked for proper charge through.
-
10-25-2012, 07:39 PM #13
Regular Guest
- Join Date
- Oct 2012
- Posts
- 10
I know a lot of times when charging a large system, the sight glass gets clear and then will start bubbling again. I charge through the low side, and flash off the refrigerant in my gauges as a liquid, let the compressor pull it in. As it gets through the condenser and receiver, the sight glass will show a solid column of liquid for a little bit, and then once more vapor gets back to the compressor, it will show more bubbles. Just keep an eye on it and see, if you didn't find any leaks, chances are there isn't a leak that large.