Page 3 of 4 FirstFirst 1234 LastLast
Results 27 to 39 of 42
  1. #27
    May 2005
    jared why not puff up the system with the 134a in it?? r22 is like gold now....
  2. #28
    r22 isn that expensive and you wont be using that much
  3. #29
    May 2005
    $ a bottle in my neck of the woods.....
  4. #30
    Oct 2012
    La Crosse, WI
    Quote Originally Posted by primmers View Post
    there was no inulation on the suction line...
    has anyone had any success with the leak sealers you blow into a system?
    I have tryed stop leak on a couple of systems, it didn't cause any problems, but it also didn't work. If the leak is that big it might not help.
  5. #31
    Oct 2008
    Ohio, USA
    We're talking about 1-2 oz max. The reason you use R22 is because most leak detectors pick it up very good.
  6. #32
    Tampa Bay, FL.
    I work on Bev-Airs everyday. Not familiar with that particular unit but sounds like a leak. Restricted condition is probably due to moisture icing up in cap tube. It's imperative to pull a deep vacuum (300-500 mics) on these systems. Break the vacuum with nitro a couple times to get there. Pull all the insulation off the line set and see if your leak is there first. I find leaks there a lot. If the copper is badly corroded, the line set should be replaced from comp to cabinet. Hope this helps.
  7. #33
    Tampa Bay, FL.
    FYI, Bev-Airs can be a PITA to leak detect. I had one this summer that got the best of me and I was forced to admit defeat and sent it to the junkyard! In my defense, it was 15 years old.
  8. #34
    May 2005
    HA! 15 year olds stuff is new in my area!!
  9. #35
    Tampa Bay, FL.
    A lot of my equipment is on or near the beach, so 15 years equals major corrosion. I forget that equipment in other climates probably fairs much better. Of course,kitchens for instance, tend to be corrosive environments no matter where you are.
  10. #36
    Feb 2007
    Georgia
    Driers warm as they pick up moisture, I think you defiantly have a leak, with POE oil and moisture you are going to be making acid big time.
    I didn't see where you had changed the drier maybe I missed that.
    You might want to look for a kink in the suction line. Look where it comes out of the cabinet, it is rare but I have seen it happen.
    Pretty sure you have some type of compound problem: low charge-leak, restriction hiside or lo side ....
  11. #37
    May 2005
    driers warm when picking up water?????? really?
  12. #38
    In a boiler room
    I was scratching my head on that one too........
  13. #39
    Lancaster PA
    Quote Originally Posted by chuckcrj View Post
    I waiting for that one to be explained.