Thread: BKV DD78/5407307 with a super heat of 74*

  1. #21
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    4,021
    Post Likes
    Pull the insulation off the suction line loop. Cap tube maybe leaking where its soldered to the suction line! Had one last week on a perlick! Took me a minute to find it. Only because i ran across the same sitiuation before that took me hours to find and lots of frustration.

  2. #22
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Merged your threads. Please don't make duplicate threads, thank you.

  3. #23
    Join Date
    May 2005
    Posts
    1,771
    Post Likes
    Thread Starter
    thanks guys...the cooler has never had any kegs in it while ive been there..

    beenthere, i deleted this thread but it wouldnt delete..

  4. #24
    Join Date
    May 2005
    Posts
    1,771
    Post Likes
    Thread Starter
    there was no inulation on the suction line...

    has anyone had any success with the leak sealers you blow into a system?

  5. #25
    Join Date
    Oct 2012
    Location
    CA
    Posts
    781
    Post Likes
    Quote Originally Posted by primmers View Post
    there was no inulation on the suction line...

    has anyone had any success with the leak sealers you blow into a system?
    Im wondering the same thing on the leak sealers .

  6. #26
    Join Date
    Oct 2008
    Location
    Ohio
    Posts
    302
    Post Likes
    Quote Originally Posted by primmers View Post
    there was no inulation on the suction line...

    has anyone had any success with the leak sealers you blow into a system?
    I would only do this as an absolute LAST resort. And after describing to the customer how much it can screw up the system.
    In fact, I actually wouldn't do this at all. Unless the customer insisted and I had a can left on the truck I was trying to use up.

    You need to determine if this thing has a leak or is just restricted. You have a good leak detector, so a shot of 22 and 150# of nitrogen you should be able to find the leak.

    As mentioned, most likely evap accumulator or evap tubing where the fins are crimped around.

  7. #27
    Join Date
    May 2005
    Posts
    1,771
    Post Likes
    Thread Starter
    jared why not puff up the system with the 134a in it?? r22 is like gold now....

  8. #28
    Join Date
    Jun 2012
    Posts
    39
    Post Likes
    r22 isn that expensive and you wont be using that much

  9. #29
    Join Date
    May 2005
    Posts
    1,771
    Post Likes
    Thread Starter
    $ a bottle in my neck of the woods.....
    Last edited by beenthere; 10-27-2012 at 09:03 PM. Reason: price

  10. #30
    Join Date
    Oct 2012
    Location
    Wisconsin
    Posts
    6,676
    Post Likes
    Quote Originally Posted by primmers View Post
    there was no inulation on the suction line...

    has anyone had any success with the leak sealers you blow into a system?
    I have tryed stop leak on a couple of systems, it didn't cause any problems, but it also didn't work. If the leak is that big it might not help.

  11. #31
    Join Date
    Oct 2008
    Location
    Ohio
    Posts
    302
    Post Likes
    Quote Originally Posted by primmers View Post
    jared why not puff up the system with the 134a in it?? r22 is like gold now....
    We're talking about 1-2 oz max. The reason you use R22 is because most leak detectors pick it up very good.

  12. #32
    Join Date
    Jun 2003
    Location
    Tampa Bay, FL.
    Posts
    151
    Post Likes
    I work on Bev-Airs everyday. Not familiar with that particular unit but sounds like a leak. Restricted condition is probably due to moisture icing up in cap tube. It's imperative to pull a deep vacuum (300-500 mics) on these systems. Break the vacuum with nitro a couple times to get there. Pull all the insulation off the line set and see if your leak is there first. I find leaks there a lot. If the copper is badly corroded, the line set should be replaced from comp to cabinet. Hope this helps.

  13. #33
    Join Date
    Jun 2003
    Location
    Tampa Bay, FL.
    Posts
    151
    Post Likes
    FYI, Bev-Airs can be a PITA to leak detect. I had one this summer that got the best of me and I was forced to admit defeat and sent it to the junkyard! In my defense, it was 15 years old.

  14. #34
    Join Date
    May 2005
    Posts
    1,771
    Post Likes
    Thread Starter
    HA! 15 year olds stuff is new in my area!!

  15. #35
    Join Date
    Jun 2003
    Location
    Tampa Bay, FL.
    Posts
    151
    Post Likes
    Quote Originally Posted by primmers View Post
    HA! 15 year olds stuff is new in my area!!
    A lot of my equipment is on or near the beach, so 15 years equals major corrosion. I forget that equipment in other climates probably fairs much better. Of course,kitchens for instance, tend to be corrosive environments no matter where you are.

  16. #36
    Join Date
    Feb 2007
    Location
    Deep South
    Posts
    355
    Post Likes
    Driers warm as they pick up moisture, I think you defiantly have a leak, with POE oil and moisture you are going to be making acid big time.

    I didn't see where you had changed the drier maybe I missed that.

    You might want to look for a kink in the suction line. Look where it comes out of the cabinet, it is rare but I have seen it happen.

    Pretty sure you have some type of compound problem: low charge-leak, restriction hiside or lo side ....

  17. #37
    Join Date
    May 2005
    Posts
    1,771
    Post Likes
    Thread Starter
    driers warm when picking up water?????? really?

  18. #38
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Quote Originally Posted by primmers View Post
    driers warm when picking up water?????? really?
    I was scratching my head on that one too........

  19. #39
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by chuckcrj View Post
    I was scratching my head on that one too........
    I waiting for that one to be explained.

  20. #40
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    maybe he meant... a drier will release moisture as it warms.

    maybe...

+ Reply to Thread
Page 2 of 3 FirstFirst 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •