Pull the insulation off the suction line loop. Cap tube maybe leaking where its soldered to the suction line! Had one last week on a perlick! Took me a minute to find it. Only because i ran across the same sitiuation before that took me hours to find and lots of frustration.
Merged your threads. Please don't make duplicate threads, thank you.
thanks guys...the cooler has never had any kegs in it while ive been there..
beenthere, i deleted this thread but it wouldnt delete..
there was no inulation on the suction line...
has anyone had any success with the leak sealers you blow into a system?
I would only do this as an absolute LAST resort. And after describing to the customer how much it can screw up the system.
In fact, I actually wouldn't do this at all. Unless the customer insisted and I had a can left on the truck I was trying to use up.
You need to determine if this thing has a leak or is just restricted. You have a good leak detector, so a shot of 22 and 150# of nitrogen you should be able to find the leak.
As mentioned, most likely evap accumulator or evap tubing where the fins are crimped around.
jared why not puff up the system with the 134a in it?? r22 is like gold now....
r22 isn that expensive and you wont be using that much
$ a bottle in my neck of the woods.....
Last edited by beenthere; 10-27-2012 at 09:03 PM. Reason: price
I work on Bev-Airs everyday. Not familiar with that particular unit but sounds like a leak. Restricted condition is probably due to moisture icing up in cap tube. It's imperative to pull a deep vacuum (300-500 mics) on these systems. Break the vacuum with nitro a couple times to get there. Pull all the insulation off the line set and see if your leak is there first. I find leaks there a lot. If the copper is badly corroded, the line set should be replaced from comp to cabinet. Hope this helps.
FYI, Bev-Airs can be a PITA to leak detect. I had one this summer that got the best of me and I was forced to admit defeat and sent it to the junkyard! In my defense, it was 15 years old.
HA! 15 year olds stuff is new in my area!!
Driers warm as they pick up moisture, I think you defiantly have a leak, with POE oil and moisture you are going to be making acid big time.
I didn't see where you had changed the drier maybe I missed that.
You might want to look for a kink in the suction line. Look where it comes out of the cabinet, it is rare but I have seen it happen.
Pretty sure you have some type of compound problem: low charge-leak, restriction hiside or lo side ....
driers warm when picking up water?????? really?
maybe he meant... a drier will release moisture as it warms.
maybe...