    Double / triple sweep?

    Does anyone actually do this? I don't see the reason for it and have been told by some its a waste of time. I've never even seen it done but I've heard people talk about it.

    Pull a vacuum and hold your microns. What are yalls thoughts on this?

  2. #2
    Join Date
    Sep 2009
    Location
    Marietta, GA
    Posts
    3,719
    Post Likes
    Its in my school book. But also your right...not many people probably do it. Loll , too much back and forth with nitro and releasing it and pulling another vacuum. It also says to just pull a deep vacuum to 500 microns and then watch if vacuum holds or see if microns go up; indicating there is maybe still moisture in the system.

  3. #3
    Join Date
    Mar 2007
    Posts
    3,824
    Post Likes
    It's a waste of time and material, IMO.
    Don't pick the fly crap out of the pepper.

  4. #4
    Join Date
    Oct 2012
    Posts
    20
    Post Likes
    It sure is a waste.

  5. #5
    Join Date
    Jun 2003
    Location
    Tampa Bay, FL.
    Posts
    151
    Post Likes
    In small,capillary refer systems; I find that it does help when I'm having trouble getting to 500 mics. May not be as useful in residential work but has definitely helped me.

  6. #6
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    Always do this on freezer equipment. Very dry Nitrogen picks up moisture more easily than straight vacuum and moisture is removed.

    Like rinsing out that milk jug before it hits the trash.

  7. #7
    Join Date
    Oct 2012
    Posts
    20
    Post Likes
    I know right?

  8. #8
    Join Date
    Sep 2012
    Location
    NW Louisiana
    Posts
    269
    Post Likes
    Quote Originally Posted by dsprice View Post
    Does anyone actually do this? I don't see the reason for it and have been told by some its a waste of time. I've never even seen it done but I've heard people talk about it.

    Pull a vacuum and hold your microns. What are yalls thoughts on this?
    I know for a fact in my area N2 purge is not done. I have had employees tell me they do not. Most don't even use a micron gauge. Its more common than you think. Same thing goes for recovery machines.

    Personally on my two HP's I installed on my new house this is how I did it. I pressure tested the line set with tracer gas, then leak checked. Each unit had 1 leak. Vented N2 and repaired. Pressure tested again with tracer, no leaks. Purged twice more with N2 then pulled vacuum down to 300 microns. The reason I was so OCD with the N2 was I roughed in my lines about 4-5 months before I installed the units. I did have them capped, but wanted to make sure they were DRY! So Basically I shot N2 through 4 times per system. One unit had about 80 ft of line set.

    CT

  9. #9
    Join Date
    Jun 2009
    Location
    Upstate SC
    Posts
    1,439
    Post Likes
    Systems that have moisture shows the greatest reward when doing a triple evacuation. It uses a lot of nitrogen but nitrogen is CHEAP and if a triple evac and sweep saves me 45 minutes pulling a vacuum then I'm game.

    Sent from my ERIS using Tapatalk 2

  10. #10
    Join Date
    May 2009
    Location
    Jacksonville FL
    Posts
    4,581
    Post Likes
    If you can pull a vacuum down to 150 microns and hold for 10 minutes....it's good.

    I would definitely recommend appion vacuum rated valve core removal tools....they allow the vacuum to be pulled in 15 minutes on residential systems. And a CPS micron gauge.

  11. #11
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    You only need to do a triple evac when your having trouble pulling down.

    If you have a very wet system, a slow low pressure purge is the best. if you shoot 400psi thru, it does no good.

    Remember, nice, SLOW, N2 purge. then re-evacuate.

    If you use a good evacuation setup it is in-fact pretty easy and fast.

  12. #12
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    just remove cores before pulling vacuum. After pulling vacuum, add Freon untill about 2 psi, remove hoses and install cores.

  13. #13
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    2,810
    Post Likes
    We always break a vacuum at least once with dry nitro after 1000 micron then pull it down again to below 500. Was taught that a very fast vac can make the moisture freeze and the dry nitro was to get it into vapor form. Might have been an old wifes tale but see no need to test the theory for $1 worth of nitro and an extra minute of time.

  14. #14
    Join Date
    Mar 2003
    Posts
    7,400
    Post Likes
    just had a job with wet system, contamination in the oil due to shietty evacuation. The so called factory expert claimed to have done "proper" evacuation in a day after repairs. We tested by doing oil analysis and megging, and made them redo it, with my guy witnessing. took four days to get the system right. first two and a half were first pull down. System was swept to 1500, broke to 2 psi, 1500, 2 psi, and finally 500. guy thought it was a waste of time too, but when checked again after charging, megger readings went up seven fold, oil analysis clean, moisture indicated very dry. He is now a believer, he says....

  15. #15
    Join Date
    Mar 2007
    Location
    AR
    Posts
    2,489
    Post Likes
    Quote Originally Posted by hydra View Post
    In small,capillary refer systems; I find that it does help when I'm having trouble getting to 500 mics. May not be as useful in residential work but has definitely helped me.
    Ditto. Seems like these systems always want to hover around 725. Putting a 1/3 hp in in the morning and will be breaking vac at least twice with n2.

  16. #16
    Join Date
    Sep 2009
    Location
    Marietta, GA
    Posts
    3,719
    Post Likes
    Quote Originally Posted by martyinlincoln View Post
    We always break a vacuum at least once with dry nitro after 1000 micron then pull it down again to below 500. Was taught that a very fast vac can make the moisture freeze and the dry nitro was to get it into vapor form. Might have been an old wifes tale but see no need to test the theory for $1 worth of nitro and an extra minute of time.

    Its true. Also can happen with oversized vacuum pump pulling deep vacuum too fast.
    Attached Images Attached Images   

  17. #17
    Join Date
    Mar 2012
    Location
    Birmingham Al
    Posts
    412
    Post Likes
    everyone is going to say this is not possible

    I have repaired at least 5 water source systems this year that had compromised coils, water flooded refrigerant systems. one had been flooded for over 1 year. Zero exaggeration. any amount of moisture can be removed dependent on how bad you want to get it out. im tired of hearing people say that if a line set is open and it rains its ruined. pull vac, break with nitro, and change oil as needed. it will come out.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •