Results 1 to 13 of 17
    Dec 2011
    San Antonio, TX
    Double / triple sweep?
    Does anyone actually do this? I don't see the reason for it and have been told by some its a waste of time. I've never even seen it done but I've heard people talk about it.
    Pull a vacuum and hold your microns. What are yalls thoughts on this?
    Sep 2009
    Marietta, GA
    Its in my school book. But also your right...not many people probably do it. Loll , too much back and forth with nitro and releasing it and pulling another vacuum. It also says to just pull a deep vacuum to 500 microns and then watch if vacuum holds or see if microns go up; indicating there is maybe still moisture in the system.
    It's a waste of time and material, IMO.
    The key to happiness is lower expectations.
    Don't pick the fly crap out of the pepper.
    Oct 2012
    It sure is a waste.
    Tampa Bay, FL.
    In small,capillary refer systems; I find that it does help when I'm having trouble getting to 500 mics. May not be as useful in residential work but has definitely helped me.
    Oct 2002
    Plano, TX
    Always do this on freezer equipment. Very dry Nitrogen picks up moisture more easily than straight vacuum and moisture is removed.
    Like rinsing out that milk jug before it hits the trash.
    Oct 2012
    I know right?
    Sep 2012
    NW Louisiana
    Quote Originally Posted by dsprice View Post
    I know for a fact in my area N2 purge is not done. I have had employees tell me they do not. Most don't even use a micron gauge. Its more common than you think. Same thing goes for recovery machines.
    Personally on my two HP's I installed on my new house this is how I did it. I pressure tested the line set with tracer gas, then leak checked. Each unit had 1 leak. Vented N2 and repaired. Pressure tested again with tracer, no leaks. Purged twice more with N2 then pulled vacuum down to 300 microns. The reason I was so OCD with the N2 was I roughed in my lines about 4-5 months before I installed the units. I did have them capped, but wanted to make sure they were DRY! So Basically I shot N2 through 4 times per system. One unit had about 80 ft of line set.
    CT
    Jun 2009
    Upstate SC
    Systems that have moisture shows the greatest reward when doing a triple evacuation. It uses a lot of nitrogen but nitrogen is CHEAP and if a triple evac and sweep saves me 45 minutes pulling a vacuum then I'm game.
    Sent from my ERIS using Tapatalk 2
    May 2009
    Jacksonville FL
    If you can pull a vacuum down to 150 microns and hold for 10 minutes....it's good.
    I would definitely recommend appion vacuum rated valve core removal tools....they allow the vacuum to be pulled in 15 minutes on residential systems. And a CPS micron gauge.
    Jul 2009
    Columbia, MD
    You only need to do a triple evac when your having trouble pulling down.
    If you have a very wet system, a slow low pressure purge is the best. if you shoot 400psi thru, it does no good.
    Remember, nice, SLOW, N2 purge. then re-evacuate.
    If you use a good evacuation setup it is in-fact pretty easy and fast.
    Oct 2002
    Plano, TX
    just remove cores before pulling vacuum. After pulling vacuum, add Freon untill about 2 psi, remove hoses and install cores.
    Jul 2010
    nebraska
    We always break a vacuum at least once with dry nitro after 1000 micron then pull it down again to below 500. Was taught that a very fast vac can make the moisture freeze and the dry nitro was to get it into vapor form. Might have been an old wifes tale but see no need to test the theory for $1 worth of nitro and an extra minute of time.