    I guess every knows that the Inducer Fan Motor is giving him a problem right now and it needs to be replaced with a new OEM motor.

    But that is not a complete repair. Again this unit has a major issue per the Trane Service Bulletin which specifically address a complete upgrade to prevent total malfunction of ALL the controls and related switches and contactors.

    Its not a big deal but if the upgrade has not been performed it is certain that he will have major problems with the remaining controls when the motor fails. There are no safety's in place which will prevent this failure and its highly possible that a fire can develop with in the controls cabinet.

    So.....The kit is available which is to alter the existing control sequence of the inducer fan motor. It includes wire harness and isolation contactor for HI and LO speeds.

    To understand it better he will have to read the service bulletin. I have one somewhere but for now here is the repair kit Lit No. which he needs to get for the repair.

    The Combustion Fan Motor Lit: RT-SVN17A-EN Dated February 20011


    __________________________________________________ _____________________________
    Troubleshooting is not part of the repair...understand the symptoms and you will find a solution.

  2. #15
    Join Date
    Oct 2012
    Location
    bayside n.y
    Posts
    4
    Post Likes
    Thread Starter
    hey the problem was the inducer motor, high speed switch was stuck closed.ended up also replacing the control board cause the relay on it had burn marks just like 2sac said,replaced it to avoid future service calls.unit is running like a champ.one question cause im new to this site.WHAT bullitin and where? some of u guys keep saying about bullitins and that they expired...where can i see them?on this site?thanks

  3. #16
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    9,123
    Post Likes
    Quote Originally Posted by tech master View Post
    WHAT bullitin and where? some of u guys keep saying about bullitins and that they expired...where can i see them?on this site?thanks
    Glad you got it resolved.

    Get your post count up to 15 and apply for pro membership. Lots of things are revealed behind closed doors in the "PRO" Forums.

    Until then, most guys will put an email address in their profile. Do you hear my foot stomping?
    Instead of learning the tricks of the trade, learn the trade.

  4. #17
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,704
    Post Likes
    Quote Originally Posted by rundawg View Post

    Until then, most guys will put an email address in their profile. Do you hear my foot stomping?
    X2
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  5. #18
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,025
    Post Likes
    expiration dates do not make any difference. they are for the manufacturer only. on some service bulletins, the experation date is for warranty claims only. but in every case, the problem still may exist and needs to be addressed.
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  6. #19
    Join Date
    Sep 2006
    Location
    Ohio
    Posts
    675
    Post Likes
    I had to replace three combustion blower assemblies in the last two months. The motors were shorted and running all the time. Another Tech just replaced one the other day at one of my accounts and none of them came with a wire harness and isolation contactor for HI and LO speeds. I was at Trane today and asked them about the service bulletin, they gave me a copy of it but didn't want to talk about it. I asked if they would replace the motors under warranty and he said I could try to. I asked why the new motors didn't come with the wire harness and isolation contactor and he said you have to ask for it. But if you didn't know about the service bulletin they weren't going to tell you.

  7. #20
    Join Date
    Mar 2008
    Posts
    284
    Post Likes
    I got copy of bulletin I could post if anyone wants it. Or should this be done in pro forum?

    Sent from my BlackBerry using Tapatalk please excuse typographical errors
    If you can not do it right, Why even do it at all?

  8. #21
    Join Date
    Apr 2012
    Posts
    87
    Post Likes
    I know this Is an old thread but can someone Email me the service bulletins you guys are talking about for the YCD units?
    I just finished cleaning up a 460v transformer mess on a YCD and found two more units on the roof that had Inducers running with no call for heat. Both units IGN boards had burnt contacts visible through the clear relay. I would have never thought about the IDM wires shorting together and causing the motor to continue to run.
    Thank you for this post

  9. #22
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    28,065
    Post Likes
    We post this stuff in the Pro forum.

    Start a thread in the pro commercial forum and call it "Trane inducer bulletin?" and someone will post it.

    The expiration of a bulletin means you get no free motor, no free kit.

    It means Trane expects the customer to now eat the cost of their defective parts.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  10. #23
    Join Date
    Mar 2014
    Location
    ohio
    Posts
    21
    Post Likes
    I agree, inducer motor. trane makes a relay kit for this, check with your local dealer for the info. they recommend you replace the motor as well.