Results 1 to 13 of 20
Thread: trane rtu model# YCD240B3HAJB
10-23-2012, 01:24 PM #1
New Guest
- Oct 2012
- bayside n.y
- 4
Hi, i was wondering if someone can shine some light on a problem im having with trane rtu unit.im new to hvac talk.model ycd240b3hajb. the induced motor is running continouasly even when t-stat is off.on a call for heat it goes throu the whole cycle and heat comes on.when it satisfies,or when u turn off heat on t-stat everything cycles off but the induced fan motor continues to run.im thinking its the ignition control board that needs to be replaced but want to confirm before i start replacing parts.could it also be the induced motor thats defective causeing it not to shut down?maybe internal switch is stuck closed in motor. any suggestions? thanks
10-23-2012, 02:03 PM #2
10-23-2012, 02:06 PM #3
As stated above, inducer motor bulletin has expired
10-23-2012, 02:14 PM #4
New Guest
- Oct 2012
- bayside n.y
- 4
serial number 346100457d. i dont think its the induced drft motor.if windings were bad motor wouldnt run at all.
10-23-2012, 02:37 PM #5
10-23-2012, 03:14 PM #6
- Mar 2011
- North Carolina Piedmont Area
- 293
Hey Rundawg, I have a job where i got 22 YCD300B4HAHB and have personally witnessed this problem. Before there was a bulletin on this, we had one unit catch on fire and we could not figure out what happened. It ended up that ALL the controls had to be replaced. It started with a bad inducer motor which shorted every control in the unit. The 460 volt transformer caught on fire. It was a mess.
It ended up after watching the other units run that the 2-speed inducer motor would short out what appeared to be between the windings of LO and HI speed. It would work fine in LO speed but when the 2nd stage of heat would come and energize the HI speed the motor would burn the windings. If you did not catch it in time the motor would short the winding and some how send line voltage back through the low voltage side (probably through the IGN Board) and fry EVERYTHING.
I think it is originally caused by a bad Run capacitor which in my case are 5 MFD / 440 Volt. And if left unnoticed the motor windings get hot when the run cap is less than 10% of it's rating.
As for the Bulletin I think Southern Mech is right that it may have expired. But this definitely must be fixed. There is a kit complete with all new wire harness, and an isolation contactor which will lock out HI/LO inducer speed or windings .
10-23-2012, 03:53 PM #7
New Guest
- Oct 2012
- bayside n.y
- 4
10-23-2012, 05:24 PM #8
10-23-2012, 06:57 PM #9
someone is not a master with the Trane YCD model.
the windings will short which makes the motor run continuous. There is a bulletin for this. you unplug hi and low from the board. if motor still runs then its the motor.
i had one also the other day.
10-23-2012, 07:07 PM #10
Im gonna N00B it up
What does it matter if the bulletin is exspired it still tells you the problem and needed test to fix it. I am geussing that the manf will not pay to fix it is what that means?
How do you get to see all these bulletins for RTU? You have to be a dealer of the manf right?
10-23-2012, 07:16 PM #11
I'm on the "inducer needs to be replaced" bandwagon. Seen this a few times. If you do a search on here you'll see a ton of threads about this.
10-23-2012, 07:19 PM #12
It's the inducer motor. First saw the problem got to be close to 8 years ago or so. Double check the relay on the ICB for burn marks, replace if necessary and don't forget to clean the burner screen. It should be plugged with cottonwood.
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
10-23-2012, 07:42 PM #13
- Jul 2010
- So-Cal
- 533
Inducer motor! and it aint cheap.