  1. #14
    Join Date
    Apr 2012
    Location
    Cape Coral Fl
    Posts
    90
    I just replaced a header coil on a unit that was 10 months old. Tubes were freezing within minutes, second stage would kick in and satisfy stat. Header was soaked. Carrier has had an issue with blocked headers.

  2. #15
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    4,195
    If they really insist on no condensation, put armaflex on the suction line and then coat the header area with spray foam. Then pray you never have clogged orifice tubes and have to replace the header

  3. #16
    Join Date
    May 2008
    Location
    United States
    Posts
    64
    I think you've already gone above and beyond what a reasonable customer would expect out of you. You're a service tech, not a design engineer for Carrier. We all know that a unit is going to have a different useful service life depending on the locale where it's installed. If I have two identical Carriers both installed at the same time, one in Houston and the other in Galveston, and they both get the same level of preventive maintenance, then I can tell you that the one in Galveston is going to have a drastically shorter service life than the one in Houston simply because the salty air is just going to destroy the coils and cabinet in a few years.

    Your customer is well aware of this, but he is the one that made the choice to buy these units from you as bid, and now he is trying to retroactively get you to make them into something they're not: super duper magic machines that will never fail and never corrode. If he's paying your company T&M for these calls, then I say yeah, try to address his concerns, but it's all gonna end in tears. You're fighting Mother Nature. Sure, you can try coating them in something to prevent further oxidation, but that's going to be all that you can do. The unit's doing what it does, and Mother Nature is doing what she does. Sooner or later, she always wins. Your enamel paint spray sounds like a good idea. I would try NuCalgon's Cold Galvanizing Spray. You could try NuCalgon's Pipe Dri on the header and suction line as well, but I've never used it and won't vouch for it.

    If, however, you guys are doing this as warranty work, then you really need to put your foot down. I seriously doubt "magic air conditioner" was written on the job proposal your company sent to the customer. You can't make every customer 100% happy 100% of the time, especially if that customer is determined to try to get more out of you than he paid for. Remove the rust that has already built up, use that galvanizing spray, then make damn sure you charge him for anything that doesn't fall explicitly under the conditions of the warranty for the duration of the warranty period, else I guarantee you he'll probably try to get every bit of free work out of you that he can until the warranty's up. And that's when he'll start calling another unsuspecting HVAC contractor to come out and service his equipment.

    Been there, done that.
    Last edited by Antarctic Fox; 10-23-2012 at 02:58 PM. Reason: added hyperlinks to products that I couldn't from my handy dandy tablet PC

  4. #17
    Join Date
    Aug 2012
    Location
    west burbs,il
    Posts
    145
    These units sweating is not abnormal. You have to make them understand that you are the professional not them in a polite manner to future customers right off the bat, its how you carry yourself. Unfornately its probably blown with this customer now that you have entertained the idea of performing a miracle.

  5. #18
    Join Date
    May 2008
    Location
    United States
    Posts
    64
    I wholeheartedly agree with you, canusayinsanity​.

  6. #19
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,667
    If I was going to install one in Galveston I would install one with an E-coated coil to make it last as long as the one 30 miles up the road in Houston.

  7. #20
    Join Date
    May 2008
    Location
    United States
    Posts
    64
    There's what you know is the right thing to do, and what the customer is willing to pay for. Give 'em two options: what you know will serve them best in the long run, and the one that's cheaper. You know which option most are gonna take. canusayinsanity hit on the crux of the matter, though.

  8. #21
    I will refrain from insulating the headers as it may become a problem in the future should it ever need service, This change out was a ASAP so the coating is scheduled to be perofrmed on the feild by a sub with microgaurd, (2 week lead time on factory coating). I had to get spot coolers to suffice in the mean time it took me get this job turned around and a crane out there to set the unit and curb adapter, curb adapter ended up being incorrectly measured as the orginal curb ended up being a mquay as opposed to the carrier one of our technicians thought it was but did not verify... had to have seacoast turn a curb around ASAP, had it in the next day had to manualy lift the unit onto the curb adapter . I'm compensated at a salary so my labor is figured as companys overhead as opposed to cost of labor. These jobs (6 so far with only 2 "small" complaints at 2 locations out 5 locations we've done replacements at so far ) have been performed on a net 45 with a 50% deposit for each change out... they still owe the other 50% so I'm sort of trying to make every effort to please them as there are six figures worth of installations and repairs to be done as awhole ( of course that is with receiving the other 50% ) and I do not mind using my time and misc materials to keep them happy after all I sold all of these change outs so it is my responsibility.

  9. #22
    Join Date
    May 2008
    Location
    United States
    Posts
    64
    In that case, I'd say to try that cold galvanizing spray.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event