    carrier 50tc - heavy condensation

    Good morning, I'm looking into a complaint of a customer recently about condensation coming off of the suction line and headers of the exposed evaporator on a carrier model 50TC-D12A2B5-0A0A0 10 ton Package RTU. I need to address it accordingly and this is the 3rd one of these i've had installed where someone noticed. Now I Belive this just to be a manufacture issue due the exposed headers from the evaporator coil sweating, however I was wondering if anyone had any ideas of possible corrections that can be done and or just refer our customer to carrier?

    any thoughts or replies are greatly appreciated.

  2. #2
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    Usually evaporators don't have insulated headers, so, is the water damaging anything? If not there is nothing wrong with the unit, just over zealous customers.

  3. #3
    Join Date
    Mar 2011
    Posts
    25
    Post Likes
    Thread Starter
    My job is to try and make the customer satisfied 100% with our installations and service, especially for the customers with multiple facillities. This units location is in a high salt enviorment as well and the condensation is leading him to belive that they wont get the proper ammount of life out of the units before the base of the package unit rust out.

    how would you in my situation address the director that is not satisfied with the ammount of water the unit is creating on the roof ?

  4. #4
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    24,816
    Post Likes
    Contact Carrier Engineering and see what they have to say.

  5. #5
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Is the unit level? So it's sweating in an exposed area of the unit like where rain would get to?

  6. #6
    Join Date
    Mar 2011
    Posts
    25
    Post Likes
    Thread Starter
    yes the unit is level, and yes in the exposed area in the compressor area, on this model the evaporator is exposed as well for whatever reason (the headers)

  7. #7
    Join Date
    May 2008
    Location
    United States
    Posts
    65
    Post Likes
    Is there something you're leaving out? This unit doesn't really look like they've changed the cabinet in going to R-22 to R-410a, so I don't see what's special about it. I believe I've run across a few 410a 50 series units in the field, but most of the Carrier 50s that I see these days are still R22 units. I've seen a lot of those, as has everyone else here who has to work on package units, and I don't think there's anything unusual about the header on the evaporator sticking into the condenser section. That's the way Carrier does it, and, of course, it's going to form condensate there. I've never seen it rust out the bottom of the condenser section in the useful service life of the unit. Beyond a "useful" service life, that's a different matter. Even then I think it's more from rainwater pooling in the condenser than condensate. Are they JUST complaining about condensate forming on the header and suction line? If that's all, then I have to agree with toocoolforschool; you've got a case of overzealous customers yanking your chain.

    Service manual for those who are interested.

  8. #8
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,043
    Post Likes
    Is this the same unit you asked about in another thread, entitled "Package RTU... Complaint from customer..."?

  9. #9
    Join Date
    Mar 2011
    Posts
    25
    Post Likes
    Thread Starter
    Name:  P82A0235.jpg
Views: 1641
Size:  53.7 KB
    Quote Originally Posted by Nuclrchiller View Post
    Is this the same unit you asked about in another thread, entitled "Package RTU... Complaint from customer..."?
    Name:  P82A0235.jpg
Views: 1641
Size:  53.7 KB

    no, we corrected that issue already... of course that unit sweats also out of the sides of the condenser/compressor compartment area... same issue same complaint

    To me it's not a big deal, but for what ever reason it is to them...

  10. #10
    Join Date
    May 2002
    Posts
    949
    Post Likes
    You could insulate the header and make it air tight.




    What about rain ,fog and morning dew?

  11. #11
    Join Date
    May 2002
    Posts
    949
    Post Likes
    Oh, and the condensation is normal.

  12. #12
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    That's pretty can I take it home??
    Costomers will try and complain about anything to get something for free, sounds like a tactic they are trying.
    Tell them it is a rooftop unit and they do not need to reengineer it for Carrier.

  13. #13
    Join Date
    Mar 2011
    Posts
    25
    Post Likes
    Thread Starter
    Quote Originally Posted by mikeacman View Post
    You could insulate the header and make it air tight.




    What about rain ,fog and morning dew?
    well i'll have to figure something out to just make them happy letting them know i'll personally go the extra mile to continue to get the jobs, even tho there is nothing wrong with the unit to begin with, i've explained that carrier has designed those that way for years and have no issue with rusting out the bottom of base of the compressor compartment area beyond a useful service life. But they've had bad experiences due to the high salt enviorment they are near they've had the same cabinents rust out within 5 years, i suggested that either epoxy paint or weatherized coating is applied to the base in an attempt to perserve the integrity. package units are inteded to be exposed to the enviorment they are just not use to the sweating because all the other units on this roof in particular are Trane with a fully encloused evap coil.

    The units have noticalbe surface rust within a week of the installation.

  14. #14
    Join Date
    Apr 2012
    Location
    Cape Coral Fl
    Posts
    186
    Post Likes
    I just replaced a header coil on a unit that was 10 months old. Tubes were freezing within minutes, second stage would kick in and satisfy stat. Header was soaked. Carrier has had an issue with blocked headers.

  15. #15
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    6,067
    Post Likes
    If they really insist on no condensation, put armaflex on the suction line and then coat the header area with spray foam. Then pray you never have clogged orifice tubes and have to replace the header

  16. #16
    Join Date
    May 2008
    Location
    United States
    Posts
    65
    Post Likes
    I think you've already gone above and beyond what a reasonable customer would expect out of you. You're a service tech, not a design engineer for Carrier. We all know that a unit is going to have a different useful service life depending on the locale where it's installed. If I have two identical Carriers both installed at the same time, one in Houston and the other in Galveston, and they both get the same level of preventive maintenance, then I can tell you that the one in Galveston is going to have a drastically shorter service life than the one in Houston simply because the salty air is just going to destroy the coils and cabinet in a few years.

    Your customer is well aware of this, but he is the one that made the choice to buy these units from you as bid, and now he is trying to retroactively get you to make them into something they're not: super duper magic machines that will never fail and never corrode. If he's paying your company T&M for these calls, then I say yeah, try to address his concerns, but it's all gonna end in tears. You're fighting Mother Nature. Sure, you can try coating them in something to prevent further oxidation, but that's going to be all that you can do. The unit's doing what it does, and Mother Nature is doing what she does. Sooner or later, she always wins. Your enamel paint spray sounds like a good idea. I would try NuCalgon's Cold Galvanizing Spray. You could try NuCalgon's Pipe Dri on the header and suction line as well, but I've never used it and won't vouch for it.

    If, however, you guys are doing this as warranty work, then you really need to put your foot down. I seriously doubt "magic air conditioner" was written on the job proposal your company sent to the customer. You can't make every customer 100% happy 100% of the time, especially if that customer is determined to try to get more out of you than he paid for. Remove the rust that has already built up, use that galvanizing spray, then make damn sure you charge him for anything that doesn't fall explicitly under the conditions of the warranty for the duration of the warranty period, else I guarantee you he'll probably try to get every bit of free work out of you that he can until the warranty's up. And that's when he'll start calling another unsuspecting HVAC contractor to come out and service his equipment.

    Been there, done that.
    Last edited by Antarctic Fox; 10-23-2012 at 02:58 PM. Reason: added hyperlinks to products that I couldn't from my handy dandy tablet PC

  17. #17
    Join Date
    Aug 2012
    Location
    west burbs,il
    Posts
    177
    Post Likes
    These units sweating is not abnormal. You have to make them understand that you are the professional not them in a polite manner to future customers right off the bat, its how you carry yourself. Unfornately its probably blown with this customer now that you have entertained the idea of performing a miracle.

  18. #18
    Join Date
    May 2008
    Location
    United States
    Posts
    65
    Post Likes
    I wholeheartedly agree with you, canusayinsanity​.

  19. #19
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    If I was going to install one in Galveston I would install one with an E-coated coil to make it last as long as the one 30 miles up the road in Houston.

  20. #20
    Join Date
    May 2008
    Location
    United States
    Posts
    65
    Post Likes
    There's what you know is the right thing to do, and what the customer is willing to pay for. Give 'em two options: what you know will serve them best in the long run, and the one that's cheaper. You know which option most are gonna take. canusayinsanity hit on the crux of the matter, though.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •