    Hi, thank you for your input.
    I have a new LENNOX HPXB15-030 HEAT PUMP WITH C33 COIL heat pump with a LENNOX G60UHV-36A-070 GAS UP FLOW FURNACE and I'm just getting familiar with it. I was wondering what the heated air output temperature should be.
    Currently outside air is 50 degrees and the output is 91 degrees. Does that sound correct?
    Cheers.
    What's the return air?
    Oct 2006
    The return air temp is 68 degrees. thx
    Jan 2003
    Kentucky
    i would tend to think all is well,because you have better than a 20 degree temperature rise between the return and supply air
    Oct 2006
    Thank you very much.
    Your air flow might be set alittle high, or could be slightly off on charge.
    I checked mine after your message. 40 out, return air 66 supply air 96. Flashing LED of variable speed blower said running 425 CFM/ton. It's always given a good temp rise.
    Oct 2006
    thanks again
    Mar 2006
    The South
    peter
    I believe a supply output temp in the low 90s with outside temp of 50 and a new HP system is on the low side and most likely reflects a refrigerant charge that needs tweaking.
    What was the outside temp when new system was charged and installed? R-22 or R-410a refrigerant?
    My opinion.