Results 1 to 13 of 13

Thread: glycol pump

  1. #1
    Join Date
    Feb 2010
    Location
    Russia
    Posts
    32

    glycol pump

    Hello!
    I need to fill an HVAC system (air handlers and fancoil units) with the propylene glycol. The system total volume is about 9000 Litres (2377.55 Gallons).
    The glycol package is a 55 Gallon Drum
    Name:  14565361.gif
Views: 640
Size:  11.0 KB

    What kind of PORTABLE pump will do the job? All I could find is Wilo-Bac
    http://productfinder.wilo.com/en/DE/...ge_description

  2. #2
    Join Date
    Dec 2010
    Location
    Down by the river
    Posts
    1,687
    Your not filling the system with straight glycol are you.

  3. #3
    Join Date
    Mar 2001
    Posts
    1,526
    I alway used a multi stage booster pump to aadd glycol to an existing system. In fact I still have it. Haven't used it in 15 years, But,,,,I have it. LOL
    One way to outthink people is to make them think you think. They'll think you're not really thinking what you're trying to get them to think you think...........

  4. #4
    Join Date
    Feb 2010
    Location
    Russia
    Posts
    32
    It is a new system and I am filling the system with the 40% water-glycol mixture. Sorry for not being clear enough.
    The points are:
    -the pump must be able to suck from the drum
    -the water-glycol mixture must be an approved fluid
    There is no need in considerable delivery head because all the units are one the same level

  5. #5
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,401
    I use a utility pump with pvc pipe ran to the bottom of the drum.

  6. #6
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    2,716
    This is what I use:
    http://www.johnstonesupply.com/store...ep?pID=W89-409

    As stated by socotech, use a piece of 3/4 pvc to dip into the drum, make sure the end of pipe your putting in is cut at a 45* angle, if just flat cut end will sometimes suck to the bottom of the drum. I have a custom made cap from another drum that I uni-bitted a hole in so I screw that into the new drum and push my 3/4 inch down in and hold it solid, also another hole in cap to allow air to enter drum.
    Need a 3/4" PVC MPT fitting so you can put a 6ft or so hose from the PVC to the inlet of pump. Out let of pump just use another hose and tie to the fill bib of the system. Make sure to prime the pump with water or whatever and your off to the races.
    Obviously if your system is piped properly should have air separators. I will usually have a ball valve before the separator to allow easy future replacement. I remove separator and throttle the ball valve until I my glycol/water mix starts burping out the top. Run the system pumps and keep burping and adding until all the air is out of system.
    If system is piped right then can be an easy straight forward process, if not...can take quite sometime to get air out of certain areas.

    Make sure your using the right glycol as specified by the manufacturer of the boiler...those new aluminum heat exchangers require a special mixture.

  7. #7
    Join Date
    Jun 2012
    Location
    Northeast
    Posts
    305
    I use a Liberty 331 utility pump and washing machine and 3/4 hoses. I can fill a 400 gallon system section in about 3-4 hours with alot of running around for changing valves and checking air venting points.

  8. #8
    Join Date
    Feb 2010
    Location
    Russia
    Posts
    32
    Thanks for advice! Very helpful.

  9. #9
    Join Date
    Aug 2006
    Posts
    2,609
    Make sure you pressure test it with air first, glycol leaks are a B**** to solder, or braze.

  10. #10
    Join Date
    Jul 2003
    Location
    Orange County N.Y.
    Posts
    1,176
    Quote Originally Posted by narkom View Post
    Hello!
    I need to fill an HVAC system (air handlers and fancoil units) with the propylene glycol. The system total volume is about 9000 Litres (2377.55 Gallons).
    The glycol package is a 55 Gallon Drum

    What kind of PORTABLE pump will do the job? All I could find is Wilo-Bac
    http://productfinder.wilo.com/en/DE/...ge_description
    I would get a positive displacement pump from Grainger, their brand is Dayton. A Taco Pony Pump is what I have on the truck and it will take down a 55 gal. drum in 5 to 10 minutes up to 15 ft. or so of head. Make a dip tube like others have said and have fun switching all of the drums.

    ...Ron
    Roof Rat

  11. #11
    Join Date
    Mar 2001
    Posts
    1,526
    Hmmm. I was doing a ten story building, thats why I had to use a booster pump.
    One way to outthink people is to make them think you think. They'll think you're not really thinking what you're trying to get them to think you think...........

  12. #12
    Join Date
    May 2010
    Location
    Canada
    Posts
    901
    I know when we fill the glycol skids on the second nature systems they want us to use distilled water. Nobody dose but I'm curious if they are asking you too as well.

    Do you have holding tanks for the system?

  13. #13
    Join Date
    Feb 2010
    Location
    Russia
    Posts
    32
    I always use a distiiled water to avoid any impurities like a chlorine. But on that site I have ready-to-use mixture.
    Yes I have holding tank.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event