    HVAC addition help for converted garage space w/ geothermal radiant - conrete floors

    I will start with background because I believe our situation is unusual: I am sorry, but this is a rather detailed and long post. [B]The essential question is in bold below./B]

    We re-purposed a 5700 sq foot solid brick warehouse with 14 ft ceilings into our home. 2500 sq feet is living space, the rest is "garage/hobby" space and is not heated or cooled.

    We have a geothermal system with radiant concrete floors in the 2500 sq ft "house" portion. The water chiller cooling and backup heat is remotely located, away from the pump itself in a large soffit like attic space above the bathroom. This is a conventional gas furnace air handler system, not the usual heat strip. The house has two total zones, one for the air and one for the floor. The air zone can operate both AC and heat. The system has a storage tank for the water and the zones are solenoid controlled with a single circulation pump.

    Existing Heating:
    The floor is the primary heater (water to water ground source), but the air handler will kick on and use the water based heat exchanger to heat the air if there is a temp drop that the floor can't catch up to immediately. (perhaps a 50 F drop overnight that levels off in the 20s F) The gas system is supposed to kick on in severe weather ( perhaps a 50 degree temp drop overnight with sustained below 0 temps) and it has, once. We also use gas manually in the first month of fall when having the thermal mass of the floor warmed up doesn't make sense yet. We could use the heat pump and water coil, but I like to experiment and see cost differences in gas vs the heat pump. Short bursts of gas are cheaper than longer bursts of electric heat pump.

    Existing Cooling:
    Cooling is exclusively done using the air handler and water chiller coil. It was able to keep up even in the worst heat wave in St Louis history without a hiccup.

    Here is the future expansion plan:
    One 432 sq ft. corner section of the "house" was never finished and does not have duct work. It is a peninsula in the structure in that it has two exterior walls and one wall that connects to the unheated garage space. One wall connects to the rest of the house and is, of course, heated. We will be turning this into our master suite. In this section the floor has its own loops that are isolated from the rest of the structure because the floor was poured at a different time, so zoning that will be simple. (there is room in the zone controller)

    I am trying to figure out some options to cover both supplemental air heat (backup and short term needs as described above) and cooling using the existing water to water heat pump. ( It was sized with this expansion in mind, so the capacity is there.) I plan to create a new zone for this section because it has very different heat losses compared to the rest of the house. The floor has a much higher ratio of exterior exposure than the rest of the house and for cooling has a much worse exposure profile as well.


    I considered extending the existing duct work and heat exchanger, but that would require a ridiculous number of electric dampers to properly create a zone, plus two fire dampers as the duct work would have to enter and exit a garage. The duct work is exposed (no attic)and fat chance of messing with the look of it anyway, says the wife.

    I thought of adding a second remote system identical to the one I have with smaller exchanger and tiny gas furnace, but I dont think there are 5000 BTU air handled furnaces.

    Chiller coils are available in many sizes for all sorts of industrial uses, so finding that isnt an issue. What I am trying to figure out is the gas backup system to use in the space. It need not be integrated with the chiller coil but it would be better to have just one blower and both systems connected to it since the chiller coil will need to do double duty. Separating them would very much complicate wiring and plumbing as well.

    Space and working conditions:
    There is no attic or basement. Part of the bathroom will have a substantial soffit over a potion of it that can accommodate a standard small house furnace/blower, etc., but shouldn't need anything that large. The garage space next door shares a wall. the garage ceiling is 14 feet high, so suspending a system and using fire dampers for 2 registers and a return is also an option. My cold air returns are actually on the ceiling because 90% of the time they are used in the summer and I plan to do this here as well. The heat pump is in that garage space so getting heat pump water and controlling cables is a snap.

    I want to avoid a heat strip, electric heat is terribly expensive and I we really don't have room in our 200 Amp electrical panel, which is why we have a gas backup for the heat pump in the first place.


    So for any of you that made it though that mess (hopefully a complete description), do you have any ideas or suggestions? The guy that installed my system originally was only supposed to be the well driller, but ended up doing the rest of it (long story). He was not that knowledgeable about the zone system and the gas backup, ( someone else did the control system) so asking him is not really an ideal approach.

  2. #2
    Join Date
    Oct 2012
    Posts
    4
    Post Likes
    Thread Starter
    I think I have a possible solution, it just popped into my head.

    Could I do this with a gas instant hot water heater and install a second water to air heat exchange coil for backup through an isolated loop? The water temps in my heat pump never get over 90F so a hot water heater would be plenty of heat.

  3. #3
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    16,674
    Post Likes
    Yea you could do that but its an expensive way to get 5k btu of auxiliary heat and it would add restriction on your duct system

  4. #4
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    16,674
    Post Likes
    A 3kw electric strip heater would suffice and they are cheap. Only if you have a 2 pole slot left in your box though

  5. #5
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    8,070
    Post Likes
    Quote Originally Posted by gonsl View Post
    I think I have a possible solution, it just popped into my head.

    Could I do this with a ... ... heater would be plenty of heat.
    See Eden Pure and other infrared heater products ...

    With these infrared products as supplemental heat, I don't know _why people wouldn't tend to use Heat Pumps more?
    ... ...
    12 hours/ day = 18 kw = $1.80 /day for 100 days = $180. per year for 1/4 to 1/2 one's house for
    perhaps a significant part of the heating season.
    ... Of course, depending on size and locale.

    _ I'm just saying .. THINK OUTSIDE THE BOX once in a while, as applicable to special situations.
    It sure beats propane and oil.
    It sure takes a lot of start -stop cycles off of heat pumps.

    _ These alteratives are safe if you select the appropriate ones ( Not the < $45 ones).

    http://www.edenpure.com/

    http://www.northerntool.com/shop/too...l&Ntt=infrared heaters&Nty=1&D=infrared heaters&Ntx=mode matchallpartial&Dx=mode matchallpartial&cmnosearch=PPC&cm_ven=google_PPC&c m_cat=HeatersStoves&cm_pla=core&cm_ite=infrared heaters&mkwid=s1NAndjZs&pcrid=12028529951&mt=e
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  6. #6
    Join Date
    Oct 2012
    Posts
    4
    Post Likes
    Thread Starter
    Ah... space heaters... functional, yes. Wife accepting the visual of a space heater? Nope, not going to happen.

    She has designed every square inch of the house and every piece of furniture is carefully chosen. Don't worry about me and having a high maintenance wife, I like how the house looks and get to build some of the furniture. I got a 48 x 44 work shop carved out of the building for myself too so I couldn't be happier!

    We have plenty of slots left in the panel, btw, but I have a shop full of welders and machinery up front that uses a 125 Amp sub panel. I guess a 15 amp 240V load wouldnt be too bad, but if the dryer, hot water heater and welder (and other shop stuff) is going all at once, lights start flickering a tiny bit already.

    [We shut the gas off over the warm season to avoid paying the $25 per month "keep it on fee" and get mostly free hot water in the summer from the heat pump, in case you were about to ask why we dont have a gas hot water heater. The gas powers a radiant heat tube in the shop and the backup gas in the winter.]
    Last edited by gonsl; 10-21-2012 at 07:57 AM.

  7. #7
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    8,070
    Post Likes
    Quote Originally Posted by gonsl View Post
    Ah... space heaters... functional, yes. Wife accepting the visual of a space heater? Nope, not going to happen.

    She has designed every square inch of the house and every piece of furniture is carefully chosen.
    Don't worry about me and having a high maintenance wife, I like how the house looks and get to build some of the furniture.

    [The gas powers a radiant heat tube in the shop and the backup gas in the winter.]
    You can hide a couple of these in the 'home-made furniture'.

    BUT, don't Ask Me.!!, how wires or noise are to be hidden.

    http://www.target.com/p/holmes-ceram...i_sku=12717351
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  8. #8
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    8,070
    Post Likes
    YES, ALL KIDDIN APPLIED .!..!!
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  9. #9
    Join Date
    Oct 2012
    Posts
    4
    Post Likes
    Thread Starter
    Quote Originally Posted by dan sw fl View Post
    You can hide a couple of these in the 'home-made furniture'.

    BUT, don't Ask Me.!!, how wires or noise are to be hidden.
    She does like to put furniture in front of outlets of course, so that part would be easy.

  10. #10
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    16,674
    Post Likes
    Edenpures don't work, it's a joke IMO. I can't believe my childhood hero Bob Vila would put his name on it... Lol.

  11. #11
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    8,070
    Post Likes
    Quote Originally Posted by jtrammel View Post
    Edenpures don't work, it's a joke IMO. Lol.
    You mean that one can hook up the electricity to a heating element and there is No heat output.

    Post # 4 stated to use a 3,000 watt element.

    That doesn't follow any thermodynamics logic.

    IT IS NOT a Joke for electricity to simply disappear.
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  12. #12
    Join Date
    Jan 2009
    Location
    Saint Joseph, MI
    Posts
    5,564
    Post Likes
    IT's not that they don;t produce heat, it that they follow hte laws of sphysics and still only produce heat at a COP of 1. Meaning that 1 Watt in rpoduces 1 Watt of heat. While infrared wavelenght energy cna make you feel warmer from a short distance away, you still need ot heat the space and a heat pump iwht a COP of 2-4, will be much cheaper to oeprate even if you need ot keep the home 2-3F warmer because thre's no infrared.

    Now, if we're comparing heat strips, to oil or propane, now the energy costs are more comparable. But then again, if your a tree hugger, since 75% of our electricity comes form fossile fuel, you want to reduce CO2 emmission, you want to use gas and oil as mcuh as possible. 80-98% efficiency when heating form those. A power plant might be 95% efficient thermally, but needs electricity to operate it's own pumps, fans, lights, etc. SO subtract all that plus the effciency of the generator and transmission, and only about I think 25-30% of the energy in fossil fuels makes it to a home. So you need a COP of maybe 4 to break even with a HE natural gas furnace.

  13. #13
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    16,674
    Post Likes
    Of course they will produce heat but they do not heat a space any more efficiently than an electric space heater.

Page 1 of 2 12 LastLast