  1. #14
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    10,478
    Post Likes
    Looks like 1.5 ton heat pump with 5kw auxiliary heat will do just fine

  2. #15
    Join Date
    Oct 2012
    Posts
    16
    Post Likes
    I don't speak HVAC, what would that equate to from a tonnage standpoint?

  3. #16
    Join Date
    Oct 2012
    Posts
    16
    Post Likes
    I have a 1.5 ton now and it can't keep my existing 750 sq ft cool when it's 95 outside. Roughly 400 sq ft of that is over an unconditioned garage.

  4. #17
    Join Date
    Jun 2012
    Location
    nampa idaho
    Posts
    66
    Post Likes
    if they dont do a manual j keep looking for good contractor

  5. #18
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    6,803
    Post Likes
    hkempf - u are running the risk of getting booted by continuing to reply in the AOP Forum.

    See Rules for "registering" in this particular forum.
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  6. #19
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    6,803
    Post Likes
    Quote Originally Posted by wraunch View Post
    I have a 1.5 ton now and it can't keep my existing 750 sq ft cool when it's 95 outside.
    Roughly 400 sq ft of that is over an unconditioned garage.
    Is that an equipment performance issue or a question of whether the area thermal envelope needs improvement?
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  7. #20
    Join Date
    Oct 2012
    Posts
    16
    Post Likes
    I believe it's an equipment issue.

  8. #21
    Join Date
    Aug 2012
    Posts
    2,937
    Post Likes
    Quote Originally Posted by wraunch View Post
    I have a 1.5 ton now and it can't keep my existing 750 sq ft cool when it's 95 outside. Roughly 400 sq ft of that is over an unconditioned garage.
    I f I had a nickle for everytime I heard that one. Unconditioned garage will increase heat load. You should look into a whisper quite unit if noise is a concern. Two stage condenser to handle extra load requirment like lots of family or electronics, this does not sound like a builder grade application.

  9. #22
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,467
    Post Likes
    Quote Originally Posted by wraunch View Post
    I believe it's an equipment issue.
    May I ask what you base that on?

    Far too easy to blame the equipment when little attention has been paid to the building envelope. It's not all about just keeping the air cool and dry. Your surroundings need to be cool as well, or you won't feel comfortable.

    Other pro responders here have already advised you to not proceed without a load calculation. I add my voice to that. Anyone who comes to your home and just "eyeballs" a guess for what you need is wasting your time, and can become an expensive mistake if you go with someone like that. Same for someone who says "oh let's just add a return here and throw a few supply registers around, everything will be cool!" No, it probably will not.

    Since you intend a home theater for the addition, you need to step up the quality of those you bring in to consult on this project. Big time.
    Building Physics Rule #1: Hot flows to cold.


    Building Physics Rule #2:
    Higher air pressure moves toward lower air pressure


    Building Physics Rule #3:
    Higher moisture concentration moves toward lower moisture concentration.

  10. #23
    Join Date
    Oct 2012
    Posts
    16
    Post Likes
    How can I check the envelope of the building? When I walk in my attic it is typically 15-20 degrees warmer than outside in the summer.

  11. #24
    Join Date
    Oct 2012
    Posts
    16
    Post Likes
    I had a company come out and recommend a Trane solution that was approx $3K more than the similar solution from American Standard. The guys I had out today use American Standard, they also mentioned that they typically use baffles and they need to do load calcs, etc. to really price it out. I liked their attention to detail much more than the guy yesterday.

  12. #25
    Join Date
    Aug 2012
    Location
    North Dakota
    Posts
    522
    Post Likes
    your 1.5 ton system may have some isues as it should not have any trouble cooling that space

  13. #26
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    10,478
    Post Likes
    The reason it won't keep up is probably because your duct work leaks and is pulling in hot attic air through the return and through leaks in the building envelope. It could also not be working properly as well (low refrigerant, low airflow etc.)