    carrier 06D drop in pressure

    drop in pressure on suction down to 15# and liquid starts at 225# run not even a minute drops down to roughly 150# thinking clog but before i tear into it any possble thoughts

  2. #2
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    4,833
    Post Likes
    Give us some more technical info


    Sent from my iPhone using Tapatalk

  3. #3
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    2,852
    Post Likes
    Need lots more info then that for diagnosis.

  4. #4
    Join Date
    Aug 2014
    Location
    RI
    Posts
    3
    Post Likes
    unit has a semi hermetic compressor was running fine had a small leak fix it did notice thermal expansion is icing up all the way to condenser to bottom of filter so replaced filter same thing and charge is correct compressor itself is over heating believe not enough refrigerant moving throu haven't delt with to many of these

  5. #5
    Join Date
    Aug 2014
    Location
    RI
    Posts
    3
    Post Likes
    what are you looking for unit has a semi hermetic compressor with suction line bypass built in txv is icing up all the way to bottom of filter dryer at the condensing coil compressor (replaced filter dryer thought it may be clogged) compressor over heating little refrig moving through