    Noisy return

    Have two returns for 2.5 ton furnace , one 8x20 , other 10 inch round. They both go to return plenum with 24x20 filter box.
    Its very loud noise coming from 12x12 return grill (10" return duct) then furnace is on . 10" round is about 25' long with four 90ties. Take off is 7x14.
    Any ideas ?
    I took filter panel off - same thing. i took furnace cover to expose fan - same thing. Something is wrong with this duct?
    Thanks

  2. #2
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,115
    Post Likes
    Quote Originally Posted by Armis View Post
    Have two returns for 2.5 ton furnace , one 8x20 , other 10 inch round. They both go to return plenum with 24x20 filter box.
    Its very loud noise coming from 12x12 return grill (10" return duct) then furnace is on . 10" round is about 25' long with four 90ties. Take off is 7x14.
    Any ideas ?
    I took filter panel off - same thing. i took furnace cover to expose fan - same thing. Something is wrong with this duct?
    Thanks
    Could you post a picture of furnace with duct work attached?

  3. #3
    Join Date
    Sep 2011
    Location
    Cotuit Ma
    Posts
    18
    Post Likes
    Thread Starter
    Name:  IMG_0712.jpg
Views: 1647
Size:  47.9 KBName:  IMG_0713.jpg
Views: 1737
Size:  46.3 KB
    Attached Images Attached Images  

  4. #4
    Join Date
    May 2009
    Location
    Cumming, GA
    Posts
    1,903
    Post Likes
    You should barely hear the system operating with properly designed ductwork.

    Assuming the blower motor and wheel are operating correctly, this system needs some ductwork modification.

    Call a pro, get a full ductwork assessment complete with CFM, FPM, and static pressure readings.

    With these readings, any decent contractor will know what needs to be done.

  5. #5
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    Quote Originally Posted by Armis View Post
    Have two returns for 2.5 ton furnace , one 8x20 , other 10 inch round. They both go to return plenum with 24x20 filter box.

    Its very loud noise coming from 12x12 return grill (10" return duct) then furnace is on a 10" round is about 25' long with four 90ties. Take off is 7x14.
    Any ideas ?
    I took filter panel off - same thing. i took furnace cover to expose fan - same thing. Something is wrong with this duct?
    Thanks
    Is there more than one Return air grille?

    If there is more than one RA grille; what percentage goes through the noisy 12X12? That is only one sq.ft., of open air area without deducting the area the grille blades block.

    If that were the only RA grille the velocity through that grille would be well over 1000-fpm; that would be over twice the velocity needed, as 400 to 500-fpm limit is required to reduce airflow noise; I'd prefer grille sizing so the velocity through the grille area(s) would not go above 450-fpm.

  6. #6
    Join Date
    Sep 2011
    Location
    Cotuit Ma
    Posts
    18
    Post Likes
    Thread Starter
    for 10" duct one 12x12 grille , for 8x20 duct - 20x16 grill

  7. #7
    Join Date
    Dec 2010
    Location
    The Quad-Cities area (midwest).
    Posts
    2,927
    Post Likes
    Quote Originally Posted by Armis View Post
    for 10" duct one 12x12 grille , for 8x20 duct - 20x16 grill
    The way the 10" flex is kinked, the 12"x12" grille (288cfm) is probably enough and not worth the bother to fix.

    The 20"x16" grille (640cfm) should be enlarged if possible. The furnace is probably moving at least 1,200cfm.

  8. #8
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    Quote Originally Posted by Armis View Post
    for 10" duct one 12x12 grille, for 8x20 duct - 20x16 grill
    Hart & Cooley Engineering Data: 12x12 has only .62-Ak or sf of free air area, & will only flow 249-cfm @400-fpm, @500-fpm it flows 311-cfm;
    @450-fpm * .62 is 279-cfm.

    The 20x16 has only 1.37-Ak, @ 450-fpm *1.37= 616.5-cfm; 500-fpm * 1.37 is 685-cfm.

    The system needs to move 1000-cfm @500-fpm or less through the RA grilles for a 2.5-ton A/C.

    311-cfm + 685-cfm = 996-cfm @500-fpm velocity through those grilles. Grilles will work if enough room behind them so there is no restriction.

    According to manual D initial velocity "through a cheap media filter" should be 300-fpm.

    When you figure using .62% for reduced free air filter area; the free air area (Ak) is 2.06 * 300-fpm = will only flow 620-cfm; therefore it could also use a larger filter area, however...

    When you divide 1000-cfm by 2.06-Ak the result is 485-fpm which is better than a lot of filter areas; so you might let it pass.

    If the other duct feeds into the 10" flex duct moving 1000-cfm is way too small; optimally it needs a 16" flex duct to get the velocity down to a little over 700-fpm. It's late & I didn't verify that situation...

  9. #9
    Join Date
    Sep 2011
    Location
    Cotuit Ma
    Posts
    18
    Post Likes
    Thread Starter
    Quote Originally Posted by George2 View Post
    The way the 10" flex is kinked, the 12"x12" grille (288cfm) is probably enough and not worth the bother to fix.

    The 20"x16" grille (640cfm) should be enlarged if possible. The furnace is probably moving at least 1,200cfm.
    Had to clarify before, 10" is solid sheet metal , not flex

  10. #10
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    Quote Originally Posted by Armis View Post
    Had to clarify before, 10" is solid sheet metal , not flex
    With a sheet metal RA duct, I'd still go with the 16" RA duct, the friction rate between flex & metal goes from 0.06 for flex to 0.02 for metal @1000-cfm of airflow volume. Either way @1000-cfm of airflow the velocity is 717-fpm.

    However, if it is flowing 1200-cfm as George2 believes, then, with (2) 90's, over 25' the friction loss is 0.03"; over 100' it would be 0.08" friction loss & either way the fpm velocity is 860. The standard is to not go over 800-fpm velocity on a Return Air duct.

  11. #11
    Join Date
    Aug 2012
    Location
    North Dakota
    Posts
    522
    Post Likes
    noisein the return usually means one thing its starved

  12. #12
    Join Date
    Sep 2011
    Location
    Cotuit Ma
    Posts
    18
    Post Likes
    Thread Starter
    I took filter panel off - same thing. i took furnace cover to expose fan - same thing. Something is wrong with this duct?
    Thanks
    Starving from what? Air ? Most of it is coming from other areas.
    Only thing to make him quiet is shut him off

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •