    When you relocated the condensing unit, how long was the system open?
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  2. #15
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Is the DTS working? Your CPR may be toast but it may be only a symptom. If DTS is stuck and not terminating defrost on temp the htrs will stay on till temp limit trips making for a hot evap then when timer times out the fans will come on. Hot evap+fans=super load. CPR may just be screaming for help. Just a thought.