    New Lennox 15.5 SEER 3 ton HVAC install and new Bradford White water heater

    The before pictures show a heat only (prepped for a/c) 70's era install with several code violations:




    The new install set on new ACX plywood:















    I know my guy's set the outdoor a/c close to the wall. Closer than I would have. Already had the talk.
    John

  2. #2
    Join Date
    Oct 2004
    Location
    Central WA
    Posts
    1,311
    How do you access the evap coil?

  3. #3
    Join Date
    Aug 2008
    Location
    San Clemente, CA
    Posts
    1,069
    We talked about it, one would have to pull fau. One of the reasons we install external TXV valves. The Pure Air pushed the evap coil up into the plenum above the ceiling. I don't anticipate anyone having to do anything with the evap coil being the air is being cleaned with a MERV 16 air filter.

  4. #4
    Join Date
    Jan 2011
    Posts
    543
    Tape between filter and furnace and coil and furnace! We use foam tape, keep it in several widths and thicknesses.

    What is the point of the trap?

  5. #5
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    5,821
    You may consider have your guys insulate the external valve. I know its not near as humid over there but it might sweat.

    Also do a little better on bulb insulation as it looks like it may also sweat a little.

  6. #6
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    3,384
    looks pretty good.

    could you not put the outdoor unit so close to the wall?

    what if you had to take the side grate off to clean it or something....it would be PITA

  7. #7
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,330
    yep not bad..... i agree condensing unit a foot to close to wall....
    it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair

  8. #8
    Join Date
    Nov 2011
    Location
    Texas
    Posts
    233
    Quote Originally Posted by JKopp View Post
    We talked about it, one would have to pull fau. One of the reasons we install external TXV valves. The Pure Air pushed the evap coil up into the plenum above the ceiling. I don't anticipate anyone having to do anything with the evap coil being the air is being cleaned with a MERV 16 air filter.
    except for those lennox coil leaks, we are a lennox dealer also
    (((PEACE IS THAT BRIEF MOMENT IN HISTORY WHERE EVERYBODY STANDS AROUND RELOADING)))

    (((YOU SEE A SIX PACK, I SEE A SUPPORT GROUP)))

  9. #9
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    4,635
    Does the gas line get bonded?

    Why is the cu bolted down? Hurricane thing?
    Which makes more sense to you?
    CONSERVATION - turning your thermostat back and being uncomfortable. Maybe saving 5-10%
    ENERGY EFFICIENCY - leaving your thermostat where everyone is comfortable. Saving 30-70%

    DO THE NUMBERS! Step on a HOMESCALE.
    What is comfort? Well, it AIN'T just TEMPERATURE!

    Energy Obese? An audit is the next step - go to BPI.org, or RESNET, and find an auditor near you.

  10. #10
    Join Date
    Aug 2008
    Location
    San Clemente, CA
    Posts
    1,069
    Quote Originally Posted by tedkidd View Post
    Does the gas line get bonded?

    Why is the cu bolted down? Hurricane thing?
    No

    It is actually in the IMC codes that mechanical equipment connected to electrical be secured in place.

  11. #11
    Join Date
    Aug 2008
    Location
    San Clemente, CA
    Posts
    1,069
    International Residential Code section M1307.2. Outdoor installations require a stable and secure installation...

  12. #12
    Join Date
    Aug 2012
    Location
    willowick ,oh
    Posts
    257
    the last time i saw that much metal tape on equipment,i took all of it out of the installers truck and gave him a caulk gun with some high temp CLEAR silicone. drives me crazy seeing all that tape. it should be caulked together as it is put together.

  13. #13
    Join Date
    Aug 2008
    Location
    San Clemente, CA
    Posts
    1,069
    That is bubble wrap over sheet metal if your talking next to the ceiling.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event