    Old Rheem - High Pressure Trips in Cooling When Overnight ODT < Setpoint

    As discussed in other threads, I've had recent issues with 1999 model Rheem HP condenser tripping high pressure switch in cooling mode. It appeared to be corrected when I switched back to a MERV 8 filter and sealed a 17cfm return leak, which may have allowed hot, moist air to enter the air handler from the attic.

    Not so corrected! The overnight temps here in Central Florida have finally started dipping below 75*, but still need cooling to maintain comfort due to high overnight humidity. I have not switched my "manual" tstat to heating, and probably won't, unless it gets really cold in January as it did 2 years ago.

    It seems if I keep the tstat at 75* during the day, then turn it down late in the evening to 72* or so, to keep it just below the overnight ODT, it keeps running like a charm, day and night. But, if i forget to lower the tstat, or don't do it until really, really late (like last night), the high pressure switch will trip if the overnight ODT is below the setpoint.

    I'll likely call my home warranty company sooner or later, if I get really tired of going out to push the red button when i forget to lower the tstat setpoint. In the meantime, does anybody have a clue as to what may be causing the high pressure switch to trip in cooling under the conditions described? I'd like to give the home warranty tech some suggestions as to what he can check, being as he likely won't be able to duplicate the conditions during daylight hours.

  2. #2
    Join Date
    Mar 2012
    Location
    West Chester, PA
    Posts
    511
    The first thing to check is if the outdoor coil is clean. These units had a habit of collecting a lot of dirt and lint on the side of the coil that is concealed by the control door.

  3. #3
    Join Date
    Aug 2012
    Posts
    2,588
    Or your cfm is failing. Either way time to bite the bullet.

  4. #4
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    6,400
    I agree, go ahead and change that thing out.

  5. #5
    Join Date
    Mar 2012
    Location
    West Chester, PA
    Posts
    511
    Why is everyone's fix to replace a 13 year old AC? HPS faults should in most cases be something that can be addressed. Maybe not by a home warranty contractor though...good luck

  6. #6
    Join Date
    Aug 2012
    Posts
    2,588
    Ummmmmm- replace condenser fan coil as needed, Then take on some type of biannual maintenance.

  7. #7
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    6,400
    Quote Originally Posted by ADillon View Post
    Why is everyone's fix to replace a 13 year old AC? HPS faults should in most cases be something that can be addressed. Maybe not by a home warranty contractor though...good luck
    Because its in south Florida, corroded and she wants a new energy efficient unit that will keep her more comfortable.

  8. #8
    Join Date
    Aug 2012
    Posts
    2,588
    sounds good to me. When in doubt change it out.
    Quote Originally Posted by jtrammel View Post
    Because its in south Florida, corroded and she wants a new energy efficient unit that will keep her more comfortable.

  9. #9
    Join Date
    Aug 2012
    Location
    Florida Space Coast
    Posts
    503
    Quote Originally Posted by jtrammel View Post
    Because its in south Florida, corroded and she wants a new energy efficient unit that will keep her more comfortable.
    Yep, sure do.

    Reset it after midnight last night and it worked all night, no problem. Was working when I left the house to go to lunch. Got back and it was off again. Reset it again, but this time the compressor fan squealed a bit but wouldn't start. So I just shut it off, put the fan on continuous, opened the windows, and called the home warranty company.

    Hoping they condemn it this time so I can get a down payment on a new unit! They put $564 into fixing leaks and changing the accumulator in July, so it's a money pit for them.

  10. #10
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    6,400
    Sounds like the fan motor is weak or stopping at times causing the high pressure trip. I wouldn't hold my breath on the home warranty co condemning the unit, they will change the motor as dumb as it is that's how they operate. Cheap cheap cheaper

  11. #11
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    6,400
    You may be able to negotiate with them for a settlement but it won't be any more than what they can get the fan motor changed for.

  12. #12
    Join Date
    Jun 2006
    Location
    Richmond, VA
    Posts
    2,843
    Quote Originally Posted by Florida Joy View Post
    Yep, sure do.

    Reset it after midnight last night and it worked all night, no problem. Was working when I left the house to go to lunch. Got back and it was off again. Reset it again, but this time the compressor fan squealed a bit but wouldn't start. So I just shut it off, put the fan on continuous, opened the windows, and called the home warranty company.

    Hoping they condemn it this time so I can get a down payment on a new unit! They put $564 into fixing leaks and changing the accumulator in July, so it's a money pit for them.
    Yes its a money-pit....and it is for them, not the warranty company you are paying the premiums to. And they have to get approval thru the company you are paying the "premiums" to. They are doomed!!!!
    Give a man a fish, he will eat for a day. Teach a man to fish, he will eat for a lifetime.

    Give a man a capacitor, doesn't know what to do. Teach a man to install it, now he knows everything.

  13. #13
    Join Date
    Aug 2012
    Location
    Florida Space Coast
    Posts
    503
    Quote Originally Posted by beshvac View Post
    Yes its a money-pit....and it is for them, not the warranty company you are paying the premiums to. And they have to get approval thru the company you are paying the "premiums" to. They are doomed!!!!
    Not sure I'm following you. Who is doomed?

    Yes, the "service provider" in the warranty company's "network" of contractors has to get approval from them before they do a repair. The warranty company paid the last "service provider" $564 and they paid another "service provider" an unknown sum in Jan 2010 to replace the TXV. They'll either pay this new "service provider" (different contractor) to fix the current problem, or they'll condemn the unit and pay me a cash-out amount so I can negotiate a replacement. Regardless, I pay the "service provider" $75 for the service call and I pay my annual premiums that cover all the other appliances, electric, plumbing, etc. in my house. So far, this home warranty company has consistently paid out more in repairs than I've paid in premiums over the past 6 years, between this house in FL and where I moved from in VA.

Page 1 of 8 12345678 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event