    Anyone know how to determine which system is bad the johnson integrater or the rs232 board in the bcu i'm getting a intermittent comm loss and have chillers cycling on and off
    KWILL or someone in blue your help would be appreciated thanks.

  2. #2
    Join Date
    Nov 2005
    Posts
    919
    Post Likes
    Commission the JCI integrater (MIG) with VT-100 thru the commission port and run the port analizer on whcih ever port you are using. This will show if you are getting data or not.
    I believe the default port data is 9600, 8 1, and none for the comm port.
    Hope this helps...
    IlovemyjobIlovemyjobIlovemyjob....say it with me now!

  3. #3
    Join Date
    Nov 2004
    Location
    Practically Canadian ehh.
    Posts
    675
    Post Likes
    Similar on Trane side. Connect to mini-monitor port and watch bacnet sends and receives. Also check rs232 cable.

  4. #4
    Join Date
    Apr 2005
    Location
    Boulder,CO.
    Posts
    566
    Post Likes
    so I can use hyper terminal for both sides of this ? thanks for the response guys.

  5. #5
    Join Date
    Nov 2004
    Location
    Practically Canadian ehh.
    Posts
    675
    Post Likes
    Yes HT works for BCU mini-monitor access.