    Quote Originally Posted by gearhead3 View Post
    ive actually had this happen almost exactly. when i would get to the site the oil pressure, level and reservoir would all be correct. i would reset sentronic and watch unit checking all operations. i found that the problem was only happening after 1:00am which is when the biggest load was coming out of defrost and also midnight crew was stocking. other techs were under the impression that customers employees were shutting off fans at night because the wif was too cold for them. which i have heard of people doing so. anyways i stayed the night because it also was a 2 hour drive. watched system in defrost and made sure no fans were being turned off. unit was a twin evap walk in freezer. ended up seeing that when coming out of defrost expansion valve on one evap coil was sticking wide open and never closing. replaced expansion valve and problem went away. also found that previous company that installed system 1) was welding with no nitrogen through lines and 2) had cut screens out of expansion valves. this was a month long head ache for our company.
    Based on the information provided, this sounds like the more likely scenario to me.

    The crankcase becoming overfull and the pump locking out on oil sound like 2 separate issues with the first being a result of the second.

    Unless you've got a suction accumilator on the rack, I'd be looking at the circuits nearest your pump as the culprit.
    "The problem is the average person isn’t tuned in to lifelong learning, or going to seminars and so forth. If the information is not on television, and it’s not in the movies they watch, and it’s not in the few books that they buy, they don’t get it" - Jack Canfield

  2. #15
    Join Date
    Oct 2011
    Location
    East Charlotte Area of NC
    Posts
    319
    Just went through all of this after a company did a refrigerant conversion on a Rack. Same time of night every 2 or 3 days there was an oil fail on a particular compressor. What we finally figured out what was happening, oil was logging in a couple of circuits at night due to low refrigerant velocities under low load conditions. This would cause the circuits to flood to the rack due to the insulation properties of the oil and low heat transfer of the evaps. Now, the case would go into defrost, oil is warm that is insulating the sensing bulb from the actual temps of the suction line.. and the circuits would flood hard trying to cool down evaporators full of oil. Now, this would wash oil from the compressor directly under this circuit, which only took about 5 mins after defrost ended. Then the oil would start coming back from the evaporators due to increased refrigerant velocities after defrost. So, everything would look good when a tech got there. Had to actually sit with it and watch it one night.

    Ended up changing 37 TXV's, but it's been purring ever since.

    Did any of that make sense?
    There's no such thing as normal,Just different kinds of crazy..

  3. #16
    Join Date
    Feb 2007
    Location
    Georgia
    Posts
    116
    It sure makes sense to me, a little low ref flow a little oil lodging a little blow by on the compressor equal big oil problems.

    I wish we knew what type and size comp he has. It seems it worked fine till now of course could have been a long term prob he has just has gotten involved in.

    If it has a helical separator it just will not work at light loads.

  4. #17
    Join Date
    Jul 2007
    Location
    Chino, CA
    Posts
    39
    maybe the oil separator isnt doing its job
    We had a very similar issue with a hill rack also about 10 years old. same senario low and med temp setup. off time for med temp and hot gas for low. ran fine for several years and all of a sudden the reservoir was empty and 1 compressor shutting off on oil failure. checked pump pressure when compressor was running 40-45 lb dif. dropped the float in the separator to see if there was a restriction and when we did almost no oil came out. usually if there is a restriction there should be enough oil to make a mess decided that the oil separator was not separating any oil. as soon as we changed the separator compressor running fine we actually had to remove a couple of gallons of oil sinse the oil was to the top sight glass

  5. #18
    Join Date
    Jun 2001
    Location
    Greeneville, Tennessee
    Posts
    331
    TChristian,

    Glad to see you posted here for answers. Thanks for posting the solution.

    I have been involved with forum since its inception and it has been a wealth of shared knowledge for all of us. Always learning!

    Douglas
    Last edited by dgruber; 01-06-2013 at 05:27 PM. Reason: misspell
    Dealing with Global Warming

  6. #19
    Join Date
    Oct 2008
    Location
    Cleveland, Ohio
    Posts
    27
    I would check how the suction group is set up depending on the operating system. I have had the same issue with CPC using there enhanced suction mode. If this compressor runs the most and is the only one at times it maybe coming back through the suction.