Results 1 to 13 of 19
    Oct 2012
    Easy Tennessee
    Need help on hill pheonix rack system
    I am working on a hill pheonix rack.One compressor on medium temp side keeps over filling with oil.this is the only compressor doing this.I have replaced the oil bowl,check valve on resivor,and replaced float in seperator.Compressor faults out every other day on oil failure at 2:30 in the morning.It is the only compressor that is overfilling with oil so I believe they have to be connected.I have noticed I can not matain oil level in resivor,oil keeps leaving resivor.If oil is going out into system why is it only overfilling the one compressor after a defrost cycle?System has 6 compressors 2 common suctions 1 on 2 low temp compressors and 1 on 4 medium temp compressors.1 common discharge header and 1 common oil return line.All pressures,tempatures,oil pressures,head tempatures,crankcase temps look good on compressors.I am lost on this though I am new to working on racks any help would be greatly appricated.It is a 2 hour drive to this store and I would love to resolve this issue.Thank's Tom
    Apr 2010
    So Cal
    Tchristian,
    I feel your pain on this one. I find oil related problems to be some of the hardest to troubleshoot. My first thought is to check the oil pressure on the comp that keeps failing. You could actually go ahead and check all of them and compare. If this particular comp appears to have low oil pressure, I would pull the oil strainer and clean. Make sure to reinstall pickup tube with slot side down. How big is the reservoir? Three gallons? I am thinking that you might be logging some of your oil in this compressor due to clogged strainer.
    Oct 2012
    Easy Tennessee
    Thank's for your reply.I have checked all 6 compressors and all are reading 53 to 58 delta p.All are copeland discus compressors.Oil seperator is 2 gallon. thanks, tom
    Apr 2010
    So Cal
    Have you been adding oil to the reservoir or is the oil coming back at some point? What kind of defrost? Are you using a sentronic ops. How do you know that it fails at 2:30? Is the rack tied to a site controller (rmcc, einstein)? I'm assuming you have low load at 2:30 am. Which compressor is this in the sequence? How long have you been experiencing the problem? How long is the defrost cycle at 2:30?
    i guess that the compressor (that fills up) is not running and that the oil is comming back from the suction line header is that possible?
    Don't interrupt me while i'm talking to myself
    Now, to the problem.
    First, since you're asking for help, you're no longer qualified to determine what is "good" and what is not. Please provide us with NUMBERS.
    Have you looked for iced up cases?
    Oct 2012
    Easy Tennessee
    Yes I have added 1 gallon of oil but it keeps leaving resivor so I quit adding.System is on a emerson control system and gives fault and time of fault and it is always between 2:30 and 2:45am everyother morning.It is a sentronic oil switch and it tripps also,The defrost is just time off defrost on medium and hot gas on low temp.This problem just started about 2 weeks ago,about the time weather started cooling off at night.Every morning I have been there the discharge is holding 200psi suction varries with load 63psi or so.Unit has 404a refrigerant,Seems like everytime compressor #3 cycles the oil level rises very slightly,I think the oil is returning through suction but Honestly im not sure.I cant understand why the other 5 compressors are not getting excess oil if it is returning through suction.Compressor #3 runs less than any of the compressors.Again I greatly appreciate your help on this issue.thank's tom
    Apr 2010
    So Cal
    Tom,
    Sorry I haven't been able to get back to you before now, but I have had a little bit of time to think over your situation. It seems as if your compressor issue and oil issue are indirectly related. I would begin by checking the problem compressor for blow by. It may be that you have blow by in the compressor causing it to shut down on the oil pressure switch. If no blow by at compressor, I would check the sentronic sensor to ensure that it is clean. The compressor doesn't typically shut down due to high oil level. At some point the sentronic has to sense low oil pressure to shut the compressor down. As an aside you can utilize equalizer lines on the compressor oil floats to keep the idle compressor from filling up with oil should a shut down ever occur. Also, check the pressure in the oil reservoir to make sure that the reservoir check valve hasn't failed (should be 5 or 20 psig above suction depending on the check valve rating). That's all I can think of for now. Good luck and let us know how it goes.
    Oct 2012
    kansas
    ive actually had this happen almost exactly. when i would get to the site the oil pressure, level and reservoir would all be correct. i would reset sentronic and watch unit checking all operations. i found that the problem was only happening after 1:00am which is when the biggest load was coming out of defrost and also midnight crew was stocking. other techs were under the impression that customers employees were shutting off fans at night because the wif was too cold for them. which i have heard of people doing so. anyways i stayed the night because it also was a 2 hour drive. watched system in defrost and made sure no fans were being turned off. unit was a twin evap walk in freezer. ended up seeing that when coming out of defrost expansion valve on one evap coil was sticking wide open and never closing. replaced expansion valve and problem went away. also found that previous company that installed system 1) was welding with no nitrogen through lines and 2) had cut screens out of expansion valves. this was a month long head ache for our company.
    Oct 2012
    Easy Tennessee
    Valves on compressor leaking by allowing the other compressors on same discharge line to push oil into compressor and overfilling the compressor with oil.in sense turning compressor into like a oil seperator on its off cycle.crankcase did not show a abnormal temp nor did the head.Im not a rack guy but this was a wild problem to figure out.has anyone ever seen this?
    Quote Originally Posted by tchristian View Post
    I've seen the problem, but I think you've got it a bit wrong.
    Valves leak by into the crankcase. This pressurizes it, stopping the rack's forced oil feed, AND, stopping the natural return of oil through the suction line and motor barrel.
    Eventually, the oil that is in the crankcase is pumped out and enters the system.
    Crankcase goes empty and compressor trips on oil.
    Now, the crankcase pressure normalizes allowing the oil that has built up in the motor barrel to drain into the crankcase, showing a much higher than normal oil level.
    Feb 2007
    Georgia
    I have also had these problems, I have seen valve plate leak during the off cycle and the flow through the compressor acts as an oil trap.
    If this is the case you could connect a gauge on the suction service valve and front seat it (make sure compressor is turned off and oil pod closed) and it will quickly rise to discharge pressure.
    If that is in fact happening a lot of oil can collect there if there are prolonged off cycles.
    As jp said it is also probably holding oil in motor compartment (due to blow by) trips oil lube control too.
    Oil problems seem to be the toughest especially hours away.