    Sporlan TEV Info

    I've got Defrost issues, Refrigeration issues, Store Manager issues....
    I suspect improper installation, but I need to prove it. Getting all lost and buried on Sporlan's website. Does anyone have info on a Y-936-AA valve? Thanks....
    The views and opinions posted here are my own. They do not reflect the corporate policies of my employer and will most likely get me fired at some point.

  2. #2
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,090
    Post Likes
    Is that a de-superheating application?

    used for liquid injection to control discharge temperature?

    that's typically where I see the "Y" valves

  3. #3
    Join Date
    Mar 2004
    Location
    Las Vegas, Nevada
    Posts
    1,647
    Post Likes
    Thread Starter
    Name:  1B Operating.jpg
Views: 345
Size:  49.5 KBName:  1B Offline.jpg
Views: 319
Size:  46.5 KB

    My thinking is either I've got a valve dumping Liquid straight down the Equalizer line, or I've got a valve designed for Hotgas Bypass incorrectly fitted to the Return as tho it were an Equalizer line.
    The views and opinions posted here are my own. They do not reflect the corporate policies of my employer and will most likely get me fired at some point.

  4. #4
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,090
    Post Likes
    Looks like your TEV is bypassing liquid into the equalizer line.

    Is that a strainer or check valve in the equalizer line?

  5. #5
    Join Date
    Mar 2004
    Location
    Las Vegas, Nevada
    Posts
    1,647
    Post Likes
    Thread Starter
    Check valve.

  6. #6
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,090
    Post Likes
    Your picture shows all kinds of problems, liquid bypassing the evaporator going into the suction line, And a check valve in the equalizer line. And this manager is giving YOU are hard time?

    Sheesh, I'm sorry for you

  7. #7
    Join Date
    Mar 2004
    Location
    Las Vegas, Nevada
    Posts
    1,647
    Post Likes
    Thread Starter
    Yeah. I'm unfamiliar with that Sporlan number. I think maybe its NOT Externally Equalized, but is designed for Gas Bypass. I think maybe someone THOUGHT it was for equalization. But I don't KNOW that. Apparently they've had problems with this case for years.

  8. #8
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,090
    Post Likes
    Welp, I guess you could look up the case model number and see if it mentions anything about a TEV with hot gas bypass.

  9. #9
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    13,155
    Post Likes
    I vaguely remember a Hussmann Y-valve like this from back around 1985. It was intended for KoolGas defrost systems. I think the side connection shown in the pics as an equalizer is intended to be routed back to the liquid line.

    Andy Schoen may know about these...unless they were before his time.

  10. #10
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    2,179
    Post Likes
    Sporlan's valve ID document says any txv preceded with a "Y" is special order made for a specific manufacturer. Most likely have to call the equipment maker to get the valve specs.

    Sent from my Transformer TF101 using Tapatalk 2

  11. #11
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    2,179
    Post Likes
    http://sporlanonline.com/210-60.pdf See page 4.

    Sent from my Transformer TF101 using Tapatalk 2

  12. #12
    Join Date
    Mar 2004
    Location
    Las Vegas, Nevada
    Posts
    1,647
    Post Likes
    Thread Starter
    Fellas - Thanks for the ideas and the link. Here's what I found:

    http://www.hussmann.com/Discontinued...TE_0358020.pdf

    What caught my eye were pages 3-1 and 3-3.
    The views and opinions posted here are my own. They do not reflect the corporate policies of my employer and will most likely get me fired at some point.

  13. #13
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    13,155
    Post Likes
    Quote Originally Posted by engineerdave View Post
    Fellas - Thanks for the ideas and the link. Here's what I found:

    http://www.hussmann.com/Discontinued...TE_0358020.pdf

    What caught my eye were pages 3-1 and 3-3.
    That's what I remember alright.

    These Y-valves were only used for cases with Koolgas and no distributor, so the TXV was internally equalized. Here's a pic I found of the Y-920:

    Name:  4315.jpg
Views: 348
Size:  13.8 KB

    I think I'd just cut all that out and replace it with a standard balanced port valve and a bypass check valve.