    I've got Defrost issues, Refrigeration issues, Store Manager issues....
    I suspect improper installation, but I need to prove it. Getting all lost and buried on Sporlan's website. Does anyone have info on a Y-936-AA valve? Thanks....
    The views and opinions posted here are my own. They do not reflect the corporate policies of my employer and will most likely get me fired at some point.
    California
    Is that a de-superheating application?
    used for liquid injection to control discharge temperature?
    that's typically where I see the "Y" valves
    Las Vegas, Nevada
    Name:  1B Operating.jpg
Size:  49.5 KBName:  1B Offline.jpg
    My thinking is either I've got a valve dumping Liquid straight down the Equalizer line, or I've got a valve designed for Hotgas Bypass incorrectly fitted to the Return as tho it were an Equalizer line.
    California
    Looks like your TEV is bypassing liquid into the equalizer line.
    Is that a strainer or check valve in the equalizer line?
    Las Vegas, Nevada
    Check valve.
    California
    Your picture shows all kinds of problems, liquid bypassing the evaporator going into the suction line, And a check valve in the equalizer line. And this manager is giving YOU are hard time?
    Sheesh, I'm sorry for you
    Las Vegas, Nevada
    Yeah. I'm unfamiliar with that Sporlan number. I think maybe its NOT Externally Equalized, but is designed for Gas Bypass. I think maybe someone THOUGHT it was for equalization. But I don't KNOW that. Apparently they've had problems with this case for years.
    California
    Welp, I guess you could look up the case model number and see if it mentions anything about a TEV with hot gas bypass.
    Jul 2000
    Cuenca EC
    I vaguely remember a Hussmann Y-valve like this from back around 1985. It was intended for KoolGas defrost systems. I think the side connection shown in the pics as an equalizer is intended to be routed back to the liquid line.
    Andy Schoen may know about these...unless they were before his time.
    Check out Icemeister's Back Room
    Read My Latest Rambling:
    What Is Mechanical Subcooling?
    ...and a new calculator:
    Nitrogen Pressure Calculator
    Jan 2010
    Sea to Sky
    Sporlan's valve ID document says any txv preceded with a "Y" is special order made for a specific manufacturer. Most likely have to call the equipment maker to get the valve specs.
    Sent from my Transformer TF101 using Tapatalk 2
    Jan 2010
    Sea to Sky
    http://sporlanonline.com/210-60.pdf See page 4.
    Las Vegas, Nevada
    Fellas - Thanks for the ideas and the link. Here's what I found:
    http://www.hussmann.com/Discontinued...TE_0358020.pdf
    What caught my eye were pages 3-1 and 3-3.
    Jul 2000
    Cuenca EC
    Quote Originally Posted by engineerdave View Post
    That's what I remember alright.
    These Y-valves were only used for cases with Koolgas and no distributor, so the TXV was internally equalized. Here's a pic I found of the Y-920:
    I think I'd just cut all that out and replace it with a standard balanced port valve and a bypass check valve.