    Quote Originally Posted by mrbean View Post
    see if you got power going to ventor motor
    Here.

    Quote Originally Posted by talktowags View Post
    I am getting no power to the plug from the board.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards". - Vernon Law

    "Never let success go to your head, and never let failure go to your heart". - Unknown

  2. #15
    Join Date
    Mar 2009
    Posts
    69
    and your point is?

  3. #16
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    16,000
    Quote Originally Posted by mrbean View Post
    and your point is?
    Point is! You said......[see if you got power going to ventor motor] He had already said.....[I am getting no power to the plug from the board] so just taking a wild guess here, if he has no power at the board, checking power to the inducer motor would be in vain.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards". - Vernon Law

    "Never let success go to your head, and never let failure go to your heart". - Unknown

  4. #17
    Join Date
    Aug 2011
    Location
    Ontario
    Posts
    381
    Sorry I am late getting in. 120v supplied to the board is through the molex connector. I have 24v at R. I have 120v at eac and motor is fine. No power to 5 pin molex when w is powered. I wired inducer to eac and it ran fine. Powered w while inducer running and would not advance to ignition or give fault code.
    There is no bad beer, some just taste better than others.

  5. #18
    Join Date
    Aug 2011
    Location
    Ontario
    Posts
    381
    There is no way to wire board wrong. Only spade connections are for the transformer.
    There is no bad beer, some just taste better than others.

  6. #19
    Join Date
    Feb 2010
    Location
    Calgary, Alberta
    Posts
    1,109
    So did we confirm if the inducer motor itself is still good?

    Had a Lennox inducer which fried the IDM relay on the board due to short to ground. The control still acted fine until it didn't see the pressure switch close.

  7. #20
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    16,000
    Never mind.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards". - Vernon Law

    "Never let success go to your head, and never let failure go to your heart". - Unknown

  8. #21
    Is there water in the trap?
    I've seen units not fire because of this, don't recall but I think the inducer at least kicked on.

  9. #22
    Join Date
    Aug 2011
    Location
    Ontario
    Posts
    381
    While I appreciate your input, you might want to read all the posts. Water in the trap ?? I hope so. A blocked trap will prevent ignition, but only after inducer starts. Any other thoughts ??
    There is no bad beer, some just taste better than others.

  10. #23
    Join Date
    Mar 2011
    Location
    Zeeland, MI
    Posts
    44
    help me understand you have the new board in it and it doesn't flash any codes? does the blower run at all with or without the fan switch "on"? and you disconnected the t-stat wire and jumped out r to w1, with 24v from r to c?

  11. #24
    Join Date
    Nov 2011
    Location
    Texas
    Posts
    316
    Well man if you have power to the board, you have 24v between C and W, and you dont have power coming out of the board, it sounds like the board to me. You bypassed the board and the inducer is operating properly, if you dont have power coming out of the board to the molex plug with a call for heat, i would say its the new board. although it is wierd the old board wouldnt bring the inducer on either, unless the is some kind of problem with those model control boards. Ive had parts come right out of the supply house faulty, its sucks when you get a sweat txv pumping down right out of the box and being careful to keep the valve cool when soldering
    (((PEACE IS THAT BRIEF MOMENT IN HISTORY WHERE EVERYBODY STANDS AROUND RELOADING)))

  12. #25
    Join Date
    Jun 2009
    Location
    Ontario, Canada
    Posts
    1,031
    ok tips of the trade: bring a cheater chord for 120v. you could test your blower (PSC only) and inducer. inducer got 120v, check your capacitor. cap OK then bring the cheater chord and test your inducer. that's the long way around. the short way is oif you got no power to the inducer then the board is pooched. if you do get power then it's the inducer. it's simple. don't think about it too much. the board is just an integrated time delay and relays, but it's ONE component. there's nothing you could change on it legally. if the board says no go the rest is no go. replace the board.
    Parts Changer Extraordinaire
    ------------------------------------------------------
    Have tools and gauges, will travel.

    RIDGID|YELLOW JACKET|UEI|TESTO|STANLEY|CPS|VETO| KLEIN|MILWAUKEE|MASTERCRAFT|

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event